    COP heatpump air/water



    Hi to everyone

    My question is about COP

    I now that the manufacturers calculate
    Different out side temp for instance
    +7, 0, -5, -10 and so on, +7 best and -10 worst COP

    But if the outside temp is
    + 7, + 10, + 15

    And we calculated

    I suppose the COP is going to decrease

    Please help me to come to conclusion
    Last edited by Seair; 18-10-2021 at 08:46 PM.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: COP heatpump air/water

    COP or coefficient of performance is a measure of energy input v energy output.
    It relates to how energy efficient the apparatus is at design conditions.
    Obviously, as outdoor temperatures increase the efficiency increases.
    Manufacturers COP figures are produced in controlled conditions and may not represent real life but allow you to make a choice when making a decision on which make to buy.

  3. #3
    Join Date
    Oct 2021
    Location
    Sweden
    Posts
    6
    Rep Power
    0

    Re: COP heatpump air/water

    Quote Originally Posted by frank View Post
    COP or coefficient of performance is a measure of energy input v energy output.
    It relates to how energy efficient the apparatus is at design conditions.
    Obviously, as outdoor temperatures increase the efficiency increases.
    Manufacturers COP figures are produced in controlled conditions and may not represent real life but allow you to make a choice when making a decision on which make to buy.

    Thanks for the answer.

    But let me give a concrete example.

    When is COP going to better? for a same model heat pump different outdoor temp.


    Heatmode
    Unit one outdoor temp +7 celsius
    Unit two outdoor temp +15 celsius

  4. #4
    Join Date
    Oct 2021
    Location
    Sweden
    Posts
    6
    Rep Power
    0

    Re: COP heatpump air/water

    Quote Originally Posted by Seair View Post
    Thanks for the answer.

    But let me give a concrete example.

    When is COP going to better? for a same model heat pump different outdoor temp.


    Heatmode
    Unit one outdoor temp +7 celsius
    Unit two outdoor temp +15 celsius
    I suppose the unit will give more heat
    But the power consumption will increase
    And COP decrease

    But i like to hear from the pro…

  5. #5
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: COP heatpump air/water

    COP not as good, but it is not “only” thing to focus on.
    heating a lot better with higher SCT
    could run less time to achieve required water temperature
    water in could also be warmer, if ambient warmer

    Heat pump in cold climate not always ideal

  6. #6
    Join Date
    Oct 2021
    Location
    Sweden
    Posts
    6
    Rep Power
    0

    Re: COP heatpump air/water

    Quote Originally Posted by RANGER1 View Post
    COP not as good, but it is not “only” thing to focus on.
    heating a lot better with higher SCT
    could run less time to achieve required water temperature
    water in could also be warmer, if ambient warmer

    Heat pump in cold climate not always ideal
    Hi my question

    is COP
    Better in 7 or better in 10 celsius

    Thanks

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: COP heatpump air/water

    Quote Originally Posted by frank View Post
    Obviously, as outdoor temperatures increase the efficiency increases.
    With more heat energy available outdoor then less energy input into the heat pump is required to achieve the required conditions indoor. This will increase the COP.

  8. #8
    Join Date
    Oct 2021
    Location
    Sweden
    Posts
    6
    Rep Power
    0

    Re: COP heatpump air/water

    Quote Originally Posted by frank View Post
    With more heat energy available outdoor then less energy input into the heat pump is required to achieve the required conditions indoor. This will increase the COP.

    I understand that, but still not have the answers i like to hear,
    The total cost for heating is decreasing when is warm outside but i like to no where is the break even.

    For instans COP at +7 is 6
    How is COP at + 14 maybe 8 or 9

    Should not increase I think

  9. #9
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: COP heatpump air/water

    .

    There is a simplistic kW in to kW out ratio but that is generally used in sales and advertising.

    The more technical would be calculations from a pH chart and that involves far too many parameters
    to be able to give you the quick answer that you want.

    The quick answer you want is "yes" if the ambient temperature rises then the COP will but only to a point
    and not under all circumstances.

    If you want water at say 45 degsC then your refrigerant in the condenser would be at least 7 or 8 degs higher
    to get the heat flow, if the system was less efficient then that difference might be near 10 or 12 degs higher.

    If you are condensing in the region of about 55 degsC average and you air ambient outside was 10 degsC
    then you would need to evaporate at about 0 degsC.

    The lift or difference between 0 degsC and 55 degsC is 55 but if you were in an outside temp of 14 degsC the the evaporator would be at about 4 degsC so the lift now or the difference now between +4 and +55 is 51.

    There is less lift so the comp won't have to work as hard and therefore the power used will be slightly less.

    The trouble is with air sourced is the ambient. The ambient very rarely stays exactly where you want it to so the COP is referred to as Energy Efficiency Ratio or EER and EER is calculated by dividing the input into the output. Because heat and electricity can both be measured in kW that means you can get a ratio of efficiency (EER) by dividing input power into output heat. The EER can now be used more realistically because EER then can allow for seasonal variations such as spring, summer, autumn and winter. Averaged over the year the EER becomes a SEER
    Seasonal Energy Efficiency Ratio. and now you have a ratio of seasonal performance that can be compared like for like with other systems.

    Not easy answer I'm affraid.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..