    Instaling VFD's on package unit



    Hii,

    I have 6 package unit Trane brand 20 Tr and it was working just fine, then I install in each one a VFD to control the airflow ( High, Med, Low ) by changing the 2 stage thermostat to Fan coil thermostat Dx.
    for the 2 first months, it was working without any issue, but recently all the units state freezing up.

    Please support me.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Instaling VFD's on package unit

    Freezing up caused by a lack of heat absorption due to low air flow

  3. #3
    Join Date
    Oct 2021
    Location
    Qatar
    Posts
    2
    Rep Power
    0

    Re: Instaling VFD's on package unit

    The problem is even with the high-speed VFD (50Hz), the coil still freezing up.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Instaling VFD's on package unit

    Are you talking about the evaporator?
    If so, you need to measure your liquid temperature before and after your metering device. You may have set the airflow too high causing excessive sub cooling.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Instaling VFD's on package unit

    If you decrease airflow over an evaporator, you then needs to reduce compressor speed accordingly and maintain an evaporation pressure above the freezing point of water.. It also is possible RH has increased these days