    Different log ph for same refrigerant



    Webp.net-resizeimage (1).gifWebp.net-resizeimage.gif
    How it comes the difference in the enthalpy for same refrigerant?


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Jan 2020
    Location
    EU
    Posts
    25
    Rep Power
    0

    Re: Different log ph for same refrigerant

    Different gas manufacturer?

  3. #3
    Join Date
    Aug 2021
    Location
    Scotland
    Posts
    14
    Rep Power
    0

    Re: Different log ph for same refrigerant

    bit hard to make out, can you point out the differences?

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Different log ph for same refrigerant

    Quote Originally Posted by skarrs71 View Post
    bit hard to make out, can you point out the differences?
    Enthalpy differs at a given pressure and temperature.. Just have a Quick look to the enthalpy scale of both
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Different log ph for same refrigerant

    Quote Originally Posted by Peter_1 View Post
    Enthalpy differs at a given pressure and temperature.. Just have a Quick look to the enthalpy scale of both
    Unfortunately the two scales are just different levels of blur.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Different log ph for same refrigerant

    .

    I think the HVAC one is wrong. the values are not the same as other comparators.

    Rob
    Last edited by Peter_1; 20-10-2021 at 08:40 PM.
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Different log ph for same refrigerant

    Sorry, hitted the wrong button first...
    I saw the same errors with R134a and R22 as well and found also errors in the calculation of Coolpack... Solkane and Coolselector gave same results where Coolpack gave complet different numbers when plotting and calculating a log p/h
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    451
    Rep Power
    17

    Re: Different log ph for same refrigerant

    Could errors from unit conversions be a possibility?

  9. #9
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Different log ph for same refrigerant

    Quote Originally Posted by Peter_1 View Post
    Sorry, hitted the wrong button first...
    I saw the same errors with R134a and R22 as well and found also errors in the calculation of Coolpack... Solkane and Coolselector gave same results where Coolpack gave complet different numbers when plotting and calculating a log p/h
    I suppose we trust the information we are using at the time.
    So if I was using Coolpack I would trust their numbers but I have sutle differences before with
    different comparators but those two you have seem to be Bars out.

    The most I have seen is a confusion between Gauge and Absolute.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..