    Pipe Sizing on Multiple Evaporators



    Hi Guys - New member, please go easy on me

    I'm doing something a little bit different; I've installed similar systems, but now working for a new employer have been asked to both design and install.

    So it's going to be a 150kw cold room; setup will be 2x 75kw systems with 5x 15kw evaporators for each unit. 5C room temp, 10k superheat, TEV & magnetic valve (each with its own controller) on each evaporator & inverter controlled condensing units to control the required load. Total Piperun 35m, and will have an 8m lift (condenser will be lower)

    I have a rough idea based on my training and literature online to judge I need 2.1/8" Suction & 7/8" Liquid, and is also the connection coming off the condensers (coincidental), but how do I determine the pipe sizes that lead to each/ evaporator?

    So, I'm expecting to use 15kw for my calculation, which gives me 3/4" & 1/2" pipework. Does this sound about right?

    Any help is much appreciated
    Last edited by Fishtank; 28-09-2021 at 01:59 PM.



  2. #2
    Join Date
    Jun 2017
    Location
    Norway
    Posts
    32
    Rep Power
    0

    Re: Pipe Sizing on Multiple Evaporators

    Download Danfoss coolselector, it will size the pipes for you

  3. #3
    Join Date
    Sep 2021
    Location
    UK
    Posts
    2
    Rep Power
    0

    Re: Pipe Sizing on Multiple Evaporators

    Quote Originally Posted by HwT View Post
    Download Danfoss coolselector, it will size the pipes for you
    Great tool - doesn't seem to allow for multiple evaporators though, so whilst it is of help, doesn't provide the full picture

  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Pipe Sizing on Multiple Evaporators

    Quote Originally Posted by Fishtank View Post
    Hi Guys - New member, please go easy on me
    I have a rough idea based on my training and literature online to judge I need 2.1/8" Suction & 7/8" Liquid, and is also the connection coming off the condensers (coincidental), but how do I determine the pipe sizes that lead to each/ evaporator?

    So, I'm expecting to use 15kw for my calculation, which gives me 3/4" & 1/2" pipework. Does this sound about right?

    Any help is much appreciated
    What size are the evaporator pipe sizes?
    Also make sure you plan for oil traps and oil return.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  5. #5
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,035
    Blog Entries
    4
    Rep Power
    31

    Re: Pipe Sizing on Multiple Evaporators

    answered wrong question

    Mod feel free to delete this
    -Cheers-

    Tycho

  6. #6
    Join Date
    Oct 2021
    Location
    London
    Posts
    1
    Rep Power
    0

    Re: Pipe Sizing on Multiple Evaporators

    I agree with this question
    Needs clarification
    What size are the evaporator pipe sizes?

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •