    Carbo Cooler relief valve



    I've got a Mojonnier Bros. carbo-cooler and need to replace the relief valve on the surge drum, but it's painted over, so I don't know the pressure setting. The Cooler is rated at 100 psi, and the surge drum is rated at 250 psi. Which setting do I need for a relief valve on the surge drum? Anyone know?

    Patrick



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    26

    Re: Carbo Cooler relief valve

    Do you have service valves in the drop leg and return line between the surge drum and carbo cooler?

    If these two items cannot be isolated, then the cooler relief valve takes precedent. Since the surge drum is rated for 250 psi, it will not hurt anything if a 100 psi relief valve is used on the surge drum.

    On the other hand, the cooler as you say is rated for 100 psi. If the cooler and surge drum can be isolated by service valves the lower design pressure is the one that controls the relief valve set pressure, or 100 psi.

    However, this is only one part of the issue. The relief valve capacity must be based on something. For the surge drum relief capacity, that's pretty simple. Now, you have to include some provision for the cooler.

    There's not really a black and white answer without more information at the present time.

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    51
    Posts
    1,630
    Rep Power
    25

    Re: Carbo Cooler relief valve

    Quote Originally Posted by flasah
    I've got a Mojonnier Bros. carbo-cooler and need to replace the relief valve on the surge drum, but it's painted over, so I don't know the pressure setting. The Cooler is rated at 100 psi, and the surge drum is rated at 250 psi. Which setting do I need for a relief valve on the surge drum? Anyone know?

    Patrick
    you could have the old valve tested to see what pressure it lifts at. Better still arrange with a valve overhall company to overhaul you valve while you wait. Pump out the MoJo, bring the valve to them, have it overhauled and tested and bring it back and fit it same or next day

    Ofcourse this does require the cooperation of the overhaul company

    There should be part numbers in the manual that came with the MoJo

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

Similar Threads

  1. Thermo-syphon Oil Cooler
    By B.B. in forum Industrial
    Replies: 5
    Last Post: 31-10-2005, 02:25 PM
  2. Water Cooler AHU's and Controls
    By Latte in forum Air Conditioning
    Replies: 6
    Last Post: 01-08-2005, 12:19 PM
  3. Relief Valve on Suction
    By Latte in forum Commercial
    Replies: 19
    Last Post: 21-01-2004, 12:57 AM
  4. over-under pressure relief valve
    By philip de moor in forum Industrial
    Replies: 3
    Last Post: 08-01-2004, 01:50 PM
  5. Pressure relief valve
    By DaBit in forum Fundamentals
    Replies: 18
    Last Post: 16-08-2003, 03:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •