    I have a mh060fxea3a with 3 unit but i have a problem the outdoor unit compresor frequency is 65hz with all 3 indoor unit on on heating mode goes up to 84hz-87hz
    Can someone make a chek on the outdoor unit with the k4 to see what value you have with all 3 unit on in cool mode
    The refrigerant pressure in cool mode with 3 unit is 8.0bar and aprox 6-7°C
    I change the 3uF cond from the outdoor fan motor......
    I change all 4 sensor from tre outdoor unit
    I charge the exact 2kg refrigerant
    I mesure the 10kohms indoor sensor
    I allso change the outdoor pcb
    Please help