    Hi guys,

    We have air handling unit (A/C system) and a thermostatic expansion valve.
    We have to fasten thermostatic bulb of expansion valve on suction pipe or should put bulb in drift of DX coil air outlet ?

    Which one is correct ?

    Thanks.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: expansion valve

    The bulb should be fastened to the suction pipe in accordance with the manufacturers instructions.

    You will find some useful information from Sporlan here, highly recommended...

    http://solutions.parker.com/Sporlanliterature
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jan 2007
    Location
    India
    Posts
    65
    Rep Power
    19

    Re: expansion valve

    It should be fixed on the suction line and has to be insulated so as to operate on right super heat