    Hi,
    I posted in earlier threat that I planned to install CW system for my residential and I worked out, needing about 5.2 KW x 4 indoor units = 20.8 KW. I have gathered all material pricing.

    Now, I need guidance if cost of Energy would be lower or Higher on CW system.

    Thanks for support in advance

    Regards
    Salman



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Energy Efficiancy Chilled Water of DX

    https://www.brighthubengineering.com...ioning-plants/

    Salman,
    Four split systems most efficient with inverter, can turn each on/off, different temperatures.
    Second central air conditioning system, less flexibility, also on inverter.
    You may have a reason for chilled water, but you do not say.
    Water has inefficientcy in temperature difference between water/refrigerant, then water to air, continuously running water pump.
    Probably Have to have a water tank, inhibitors etc

  3. #3
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: Energy Efficiancy Chilled Water of DX

    Hi,
    Reason for Chilled water is that it's easier to mantain. I would have only 1 central compressor /condenssor to take care off.

    Single AC system units of made in china are not reliable as quality of tubes are very low and have lot of problems every season, despite the fact that it's heavily used in Pakistan.
    My plan to is to have inverted based compressor when number of FCU would be less in operational.

    Currently electricy cost in Pakistan is USD 0.16 / KW which is heavy on pocket.
    I can apply same unit for Dx system, but it would be very difficult for me to mantain, so now I need suggestion that with high eelctricity cost cmpare to chiller system, is it worth taking decission.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Energy Efficiancy Chilled Water of DX

    Would the addition of solar PV panels to power the secondary CW side be an option perhaps to keep down electrical running costs?

    I appreciate that the initial costs can be high.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Energy Efficiancy Chilled Water of DX

    AC DX evaporators usually operate between 5 and 8 deg C. They both reduce air temperature and extract moisture but the control arrangement addresses temperature alone. To run water to air exchangers at the same temperatures means the water to refrigerant heat exchanger (evaporator) is going to operate very close to freezing temperatures...the system will need more protection and better controls than a regular AC split.

  6. #6
    Join Date
    Feb 2015
    Location
    Pakistan
    Age
    47
    Posts
    67
    Rep Power
    10

    Re: Energy Efficiancy Chilled Water of DX

    Thanks, but controlling water to 5.0 C is very easy. Any temp controller can do it.
    The problem is running cost. I dont know if running cost is high or low.