    Swing compressor dual hp switches setup.



    Good morning ladies and gentlemen.

    I have a GEA LT screw in a swing configuration. In LT mode the discharge feeds a open type flash intercooler. MT modes feeds the cooling towers.
    LT -38c /-10c
    MT -10 / 32c

    Valves are manually changed between LT and MT. LT hp setting is set for 13.4b and the MT hp set for 19.7b.

    I have a fellow colleague saying that both hp switches should set for the lowest value. I have scoured the internet trying to find a “good working practice” for swing compressor operation. I cannot find any source(s) as to why this needs to be the case.

    I thought I would open this up to like minded individuals who could light the way....

    Many thanks



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Swing compressor dual hp switches setup.

    What are the switches operating?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Apr 2021
    Location
    United Kingdom
    Posts
    2
    Rep Power
    0

    Re: Swing compressor dual hp switches setup.

    HP safety switch...

  4. #4
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    451
    Rep Power
    17

    Re: Swing compressor dual hp switches setup.

    What are the PRVs pressures?

  5. #5
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Swing compressor dual hp switches setup.

    jjgixer,
    Normally HP trip settings are 10-15% lower than lowest relief valve for that part of system
    Interstage/High stage.

    Other things to consider is relief between compressor discharge to suction, HP should be below this
    Local compressor pressure transducers
    Any other HP protection, like a hardwired pressure switch, most common is Danfoss KP7ABS dual protection switch.

    So in order compressor unloads on high pressure or high motor amps/ local transducer trip/hard wired pressure switch trip, which stops starter/internal relief valve opens/relief to atmosphere, last line of safety protection.

    I think in UK would be similar

    In your case I would try to set at lower setting, as what scenario would you want compressor to be running up to 19.7 bar when design of 32 SCT 1.136 bar.

    You need to check all relief settings on plant to make informative decision.

    Most compressor manufacturers have high relief settings on packages so to meet most design scenario's, does not mean you have to set it that high.
    Last edited by RANGER1; 28-04-2021 at 09:39 PM.