    Mitsubishi PUHZ-ZRP140VKA condenser



    Hi all, a small shout for help please.
    I have a Mitsubishi AC that keeps freezing up.

    The condenser is turning into a solid block of ice and smashing up the fan blades. No fault codes, it will just run untill the damage is done!

    If the site are using the AC on constant heating mode, do Mitsubishi have a internal defrost command ? If so what thermistor activates this?

    TIA for any help



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Mitsubishi PUHZ-ZRP140VKA condenser

    Lots of things to check:

    Gas charge
    Outdoor thermister values
    Coil thermister values
    Etc.

    Here's a link to the Service Manual http://www.mitsubi****ech.co.uk/Data...SM_OCH527C.pdf

  3. #3
    Join Date
    Mar 2006
    Location
    Midlands
    Posts
    29
    Rep Power
    0

    Re: Mitsubishi PUHZ-ZRP140VKA condenser

    Cheers Frank, I suspected thermistor issues, as someone has butchered it before! Sorry, I can't open the attachment!

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Mitsubishi PUHZ-ZRP140VKA condenser

    It's a web site link not an attachment. Looks like it didn't paste correctly. I'll have a look
    Last edited by frank; 27-04-2021 at 05:30 PM.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: Mitsubishi PUHZ-ZRP140VKA condenser

    It's the site language editor that does it Frank, your link was fine before the astericks struck.

    Try this https://tinyurl.com/9x9m7za5
    Last edited by Brian_UK; 27-04-2021 at 07:10 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,044
    Rep Power
    35

    Re: Mitsubishi PUHZ-ZRP140VKA condenser

    Outdoor coil probe main suspect if not going into defrost.

  7. #7
    Join Date
    Mar 2006
    Location
    Midlands
    Posts
    29
    Rep Power
    0

    Re: Mitsubishi PUHZ-ZRP140VKA condenser

    Thankyou Brian, I've got the info downloaded 👍🏼

    Tayters, again thanks, I think we're on the same page. Thermistor issues.

    I was unsure as the weather or not, the condenser still defrosted its self when on "heat mode" or "auto cycle" I guess if the coil probe is reading correctly, it should defrost either way ?