    Dear friends,
    I heard cooling capacity of compressor with same displacement in R22 is similar to NH3 (R717) but when I compare heat latent of NH3 and R22 they are very different, NH3 is about 1300 Kj/Kg and for R22 is about 200 Kj/Kg.
    Would it be possible someone help me to compare these two refrigerants from cooling capacity aspect of view ?
    Thanks in advance.
    3,355
    Re: NH3 against R22
    Quote Originally Posted by skyboy6142 View Post
    Dear friends,
    Thanks in advance.
    Skyboy,
    If it was a Mycom 200VLD compressor - 10 deg C sst 35 deg C sct
    Nh3 821kw 203kw absorbed power
    R22 792 kw 209 kw
    R22 much denser refrigerant
    So same in this case
    https://agilityrefrigeration.weebly....monia-vs-*****
    Jan 2006
    Croatia
    68
    2,261
    31
    Re: NH3 against R22
    Hi skyboy6142,
    Dear friends,
    Thanks in advance.
    something from your neighborhood ...
    Best regards, Josip
    Sep 2009
    Iran
    66
    672
    1
    Re: NH3 against R22
    In low temperature R22 has more efincy than NH3
    Jun 2020
    Malaysia
    44
    Re: NH3 against R22
    Thanks from all of you
    Jun 2006
    SPAIN
    49
    13
    Re: NH3 against R22
    Skyboy,
    With an open piston compressor no cooling at all. At same regime -15 ºC / +35 ºC, both @ 1,000 rpm
    R22 - 335,2 kW @ 117,7 kW absorb power.
    R717 (NH3) - 335,5 kW @ 106,3 kW absorb power.
    And then discharge temperature on R717 will be much higher.
    Just remember GWP of R717 = 0, R22 = 1,810...
    I hope with this you don't even keep thinking on using R22.
    Take care...
    D