    NH3 against R22



    Dear friends,

    I heard cooling capacity of compressor with same displacement in R22 is similar to NH3 (R717) but when I compare heat latent of NH3 and R22 they are very different, NH3 is about 1300 Kj/Kg and for R22 is about 200 Kj/Kg.
    Would it be possible someone help me to compare these two refrigerants from cooling capacity aspect of view ?

    Thanks in advance.



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: NH3 against R22

    Quote Originally Posted by skyboy6142 View Post
    Dear friends,

    I heard cooling capacity of compressor with same displacement in R22 is similar to NH3 (R717) but when I compare heat latent of NH3 and R22 they are very different, NH3 is about 1300 Kj/Kg and for R22 is about 200 Kj/Kg.
    Would it be possible someone help me to compare these two refrigerants from cooling capacity aspect of view ?

    Thanks in advance.
    Skyboy,
    If it was a Mycom 200VLD compressor - 10 deg C sst 35 deg C sct

    Nh3 821kw 203kw absorbed power
    R22 792 kw 209 kw
    R22 much denser refrigerant

    So same in this case

    https://agilityrefrigeration.weebly....monia-vs-*****
    Last edited by RANGER1; 03-04-2021 at 08:27 PM.

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: NH3 against R22

    Hi skyboy6142,
    Quote Originally Posted by skyboy6142 View Post
    Dear friends,

    I heard cooling capacity of compressor with same displacement in R22 is similar to NH3 (R717) but when I compare heat latent of NH3 and R22 they are very different, NH3 is about 1300 Kj/Kg and for R22 is about 200 Kj/Kg.
    Would it be possible someone help me to compare these two refrigerants from cooling capacity aspect of view ?

    Thanks in advance.
    something from your neighborhood ...
    https://agilityrefrigeration.weebly....monia-vs-*****


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: NH3 against R22

    Hi
    In low temperature R22 has more efincy than NH3

  5. #5
    Join Date
    Jun 2020
    Location
    Malaysia
    Posts
    44
    Rep Power
    0

    Re: NH3 against R22

    Thanks from all of you

  6. #6
    Join Date
    Jun 2006
    Location
    SPAIN
    Age
    48
    Posts
    13
    Rep Power
    0

    Re: NH3 against R22

    Skyboy,

    With an open piston compressor no cooling at all. At same regime -15 ºC / +35 ºC, both @ 1,000 rpm
    R22 - 335,2 kW @ 117,7 kW absorb power.
    R717 (NH3) - 335,5 kW @ 106,3 kW absorb power.

    And then discharge temperature on R717 will be much higher.

    Just remember GWP of R717 = 0, R22 = 1,810...

    I hope with this you don't even keep thinking on using R22.

    Take care...