    Master Cella controller problem



    New here, coming with very strange problem:
    On Master Cella programmer temperature display works fine until defrost starts, then temp display remains (-22) despite rising temp in the chamber. Only switching off and back on complete controller brings the real temp value and controller starts working again.
    Any ideas or hints ?



  2. #2
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    452
    Rep Power
    17

    Re: Master Cella controller problem

    Have a look at the controllers parameter settings, there may be one for what is displayed during defrost. It will probably be set to display the temperature the chamber was at before the defrost started, and then only show the real chamber temperature once defrost has finished and the chamber has got back down to the set point.

  3. #3
    Join Date
    Apr 2021
    Location
    Poland
    Posts
    2
    Rep Power
    0

    Re: Master Cella controller problem

    Quote Originally Posted by seanf View Post
    Have a look at the controllers parameter settings, there may be one for what is displayed during defrost. It will probably be set to display the temperature the chamber was at before the defrost started, and then only show the real chamber temperature once defrost has finished and the chamber has got back down to the set point.
    thx for your reply seanf. I was not clear in my initial post - defrost ends up but system does not restart cooling afterwards. only hard reset brings all back to normal functioning until next programmed defrost cycle

  4. #4
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    452
    Rep Power
    17

    Re: Master Cella controller problem

    I would be making sure all the controllers parameters are set to something suitable to the application, including the drip down time/delay of start up after defrost parameter, making sure nobody has been playing around with the settings. After that I guess you would make sure it is the controller that is the problem, checking there is no output to the compressor/liquid solenoid after the defrost and drip down has finished.

  5. #5
    Join Date
    Jun 2005
    Location
    Malaysia
    Posts
    28
    Rep Power
    0

    Re: Master Cella controller problem

    Quote Originally Posted by Tomaszek View Post
    New here, coming with very strange problem:
    On Master Cella programmer temperature display works fine until defrost starts, then temp display remains (-22) despite rising temp in the chamber. Only switching off and back on complete controller brings the real temp value and controller starts working again.
    Any ideas or hints ?
    Hi There,
    the problem is Parameter d6 is set to Lock the temperature when defrosts,
    Press "set"for 5 Sec and go to Parameter "d6 Terminal display during defrost" and Set it to "0" as 0 = Temperature alternating with dEF

    The default for d6 is "1 = Display disabled"

  6. #6
    Join Date
    Sep 2021
    Location
    US
    Posts
    1
    Rep Power
    0

    Re: Master Cella controller problem

    Quote Originally Posted by w.l.ong View Post

    The default for d6 is "1 = Display disabled"
    Tried this with no luck... Can it be the other reason?

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Master Cella controller problem

    The display doesnt start to record the actual room temp after defrost until set point is reached.