Results 1 to 3 of 3
  1. #1
    Join Date
    Mar 2021
    Location
    Belize
    Posts
    1
    Rep Power
    0

    York Chiller YCIV Suction Pressure Limiting



    Hi Guys

    Please see below data if anything seems abnormal:

    System running at 100%
    PRESSURES
    Suction = 26 Oil = 177 PSIG
    Discharge = 192 PSIG

    TEMPERATURES
    OIL = 123.4
    SUCTION = 43.5 F
    DISCHARGE = 159.4 F

    SUCTION
    TEMP = 43.9
    SUPERHEAT = 13.2 F
    SAT TEMP = 30.7 F

    DISCHARGE
    TEMP = 159.5 F
    SUPERHEAT = 32.2 F
    SAT TEMP = 127.3 F

    MOTOR TEMPS
    T1 = 120.5 F
    T2 = 134.6
    T3 = 95.6 F

    FLASH TANK
    LEVEL 29.4
    FEED VALVE PERCENT OPEN = 46.4

    SUCTION SUPERHEAT = 15.1
    DRAIN VALVE OPEN = 54.7

    CHILLER WILL SOMETIMES JUST SHUTDOWN AND NOT GIVE ANY ERRORS..WHAT AM i MISSING GUYS

    Picture 014.jpg



  2. #2
    Join Date
    Jul 2007
    Location
    LIbya
    Age
    58
    Posts
    72
    Rep Power
    17

    Re: York Chiller YCIV Suction Pressure Limiting

    pleas what is the application that this chiller is intended for?

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: York Chiller YCIV Suction Pressure Limiting

    Discharge pressure looks high!