    Daikin Piping Layout Confirmation and BS Box Count



    Unit is a RWEYQ72PCTJ with three AHUs and one BS Box. This was my first commission with a heat recovery Daikin and received a UF error. I suspect the system may be piped incorrectly and attached some layout diagrams. Anyone confirm?

    Also, I was able to count the number of AHUs and 3 were confirmed via the LEDs. When I entered the mode to count the BS Box, the LEDs showed 3 boxes when only one is installed. Very odd as HP7 should only be illuminated. Bug perhaps?
    Attached Images Attached Images



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin Piping Layout Confirmation and BS Box Count

    Error UF comes up as Indoor Unit failed to get address from Outdoor Unit.

    Sounds like a wiring issue rather than a piping issue.

  3. #3
    Join Date
    Feb 2015
    Location
    USA
    Posts
    14
    Rep Power
    0

    Re: Daikin Piping Layout Confirmation and BS Box Count

    When all of the equipment is turned on, Daikin finishes the addressing procedure when the HP2 LED goes out, right? I was able to initiate the first test run but it obviously failed.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin Piping Layout Confirmation and BS Box Count

    If the outdoor unit cannot 'handshake' the indoor unit then that is due to a lack of communication. This could be caused by a lack of power supply to the indoor unit, a fault in the F1 F2 wiring or failed indoor pcb.

    A piping error would show up when the initial 'Test' run is carried out.

    The initial addressing proceedure will only address indoor units the outdoor can 'see'.