    York YMWA CO 45 chiller Er01



    20210115_070526.jpg20210115_070526.jpgHello,

    I got a problem with a York chiller, which has error Er01 - error digital HP.
    the controller it is SBW655/C/S with SE600 Energy and XVR for electronic TXV.
    I tried to mount a new SBW655 controller , factory configured for this application by Johnson controls and the same error occur. The HP and LP sensors are switch type, no reset button for HP. The sensors for HP and LP provide a NC contact. The R410A ***** pressure in static it is 12,5 bar, this chiller it is mounted inside to a building. The condenser it is a plate heat exchanger with water flow from client water tank with external pump. I checked the CL and AL parameters for both controller and they are the same, but the new one doesn't start the pump for evaporator, and the initial controller after evaporator pump start the compressor enter in preparing, flashing the compressor led light, but the error er01, correspond to AL10, error Er01, disable the compressor.
    Have anyone any idea?
    Initial company service technician insert the relay and the coil pin was bended, i straighten it and the relay powers and the contacts are closed(refering the k1 relay from attached schematic
    Attached Images Attached Images
    Last edited by serginno; 22-01-2021 at 09:03 AM. Reason: completing new information



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: York YMWA CO 45 chiller Er01

    Relay may be powered but is the output showing NC with your multimeter?

    Sounds like a wiring issue to me
    Last edited by frank; 22-01-2021 at 04:21 PM. Reason: Typo

  3. #3
    Join Date
    Jun 2009
    Location
    Romania
    Age
    46
    Posts
    5
    Rep Power
    0

    Re: York YMWA CO 45 chiller Er01

    Yes , it does, the two contact are one to put the DO6 to the same potential with Neutral port, and one for DI2 to GND.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: York YMWA CO 45 chiller Er01

    DO6 - Digital Output 6
    DI2 - Digital Input 2

    Are you sayiny that you have a wire coming out of DO6 into the relay and then into DI2 from the relay?

  5. #5
    Join Date
    Jun 2009
    Location
    Romania
    Age
    46
    Posts
    5
    Rep Power
    0

    Re: York YMWA CO 45 chiller Er01

    No, What i`m saying is that the relay has 2 pair of contacts one pair related to DO6 and one to DI2.

  6. #6
    Join Date
    Jun 2009
    Location
    Romania
    Age
    46
    Posts
    5
    Rep Power
    0

    Re: York YMWA CO 45 chiller Er01

    I solved the problem with the chiller, the DI2 was burn, and the 20th pins connector have the pins enlarged and doesn`t made electrical connection.20210209_091737.jpg

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: York YMWA CO 45 chiller Er01

    Good find. Always a pleasure in finding the cause and fixing it.

    Thanks for the update.