    Split or cracked flare nut on expansion valve



    I have a small cold-room with a thermostatic expansion valve, the liquid line 3/8 flare nut keeps cracking after about 8 months, I have tried different expansion valve seats and have not over tightened the nut could anyone give some advise why this may be happening.



  2. #2
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: Split or cracked flare nut on expansion valve

    Valve incorrect position and allowing water on the threads then cracks or perhaps unit passing a bit to much liquid danfoss do a dedicated orifice flare nut with a flat orifice that has cut outs in the threads to reduce freeze crack ive never had one leak yet

  3. #3
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Split or cracked flare nut on expansion valve

    .

    There are also two types of valve.

    One has a flare nut connection on both the inlet and outlet and the other has a brazed outlet
    with a different type of nut for the orifice inlet side.

    So as Charlie states the position of the valve is a factor and also the selection.

    There are also two types of flare nut.

    One is a long body and the other is a short body. If they are at risk of ice damage then
    using the smaller flare nut might make a difference.

    Regards
    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..