  1. #1
    SPR's Avatar
    SPR Guest

    Pipe runs



    Can anyone tell me what symptons that would be likley to occur if the pipe runs to a remote condenser were to long, the problem i have is with Liebert close control units, i'm convinced that the runs are to long (about 75-90 Meters mostly verticle) there have been so many problems with these units that it would to many to list so i was wondering what sort problems would arise from the pipe runs being to long.



  2. #2
    Join Date
    Mar 2006
    Location
    Norfolk
    Posts
    160
    Rep Power
    19

    Re: Pipe runs

    Hi

    The most likely problem would be pressure loss.

    This site is very useful:-

    http://www.pressure-drop.com/

  3. #3
    Join Date
    Mar 2005
    Location
    u.a.e
    Age
    68
    Posts
    169
    Rep Power
    20

    Re: Pipe runs

    If refrigeration piping is not designed properly with long runs you have pressure drop problem as Paulajayne said and also you will face oil problems.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Pipe runs

    The pressure loss is only one part of the problem.

    Excess pressure loss also affects the quality of the liquid flowing to the expansion valves. Without sufficient liquid subcooling, the refrigerant will flash off. This lowers the amount of liquid feeding the expansion valves and reduces the cooling capacity.

    If the suction lines are not sized properly, you can loose the oil return back to the compressors, or have excessive suction line pressure loss. This affects the compressor capacity also.

    It's not so much the piping length as it is probably due to improperly selected tubing diameters, poor installation of the tubing, and other contributing factors.

    One other thing: Long suction lines can absorb a lot of heat if the lines are not insulated properly. The additional heat gain can increase the motor and discharge temperatures also. Neither of these are desired.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Pipe runs

    (about 75-90 Meters mostly verticle)
    Thats some large building

  6. #6
    SPR's Avatar
    SPR Guest

    Re: Pipe runs

    cheers guy's for replies, and yes Frank it is a very large buiding.

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Pipe runs

    I'm sorry to say I did not catch the "mostly vertical" part. That's a good call Frank.

    If indeed the pipe runs are mostly vertical; which line runs up and which one runs down?

    Each presents it own set of unique problems.

  8. #8
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Question Re: Pipe runs

    Liebert Hiross?

    Renato

  9. #9
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    21

    Re: Pipe runs

    And, there possibly may have been a need for oil-trap bends on the climb, to help the oil get around. Worth getting a sketch off to the technical dept of Liebert, with pipe sizes and the height changes, and ask what should have been installed in this respect. Maybe nothing, but possibly they were needed.

    {And maybe this aspect is nothing to do with your system's symptoms.}

  10. #10
    Join Date
    Feb 2008
    Location
    Wellingborough
    Age
    56
    Posts
    35
    Rep Power
    0

    Re: Pipe runs

    If it is a Liebert Hiross or Emerson Networ Power unit, your installation is outside of the manufacturers maximum pipe run recommendations of 50m. Any installation outside of this recommendation needs to be technically validated where you would be advised of the pipe sizes required & more than likely the need for an oil separator.

  11. #11
    oby1's Avatar
    oby1 Guest

    Re: Pipe runs

    Quote Originally Posted by Tiesse View Post
    If it is a Liebert Hiross or Emerson Networ Power unit, your installation is outside of the manufacturers maximum pipe run recommendations of 50m. Any installation outside of this recommendation needs to be technically validated where you would be advised of the pipe sizes required & more than likely the need for an oil separator.
    Hello everyone,
    I have a question about sizing route for a cold Emerson Liebert Hiross, HPM model S10OA.In technical specifications of products, we recommend a cold trail, diam.12 liquid, gas diam.12 up to 50 meters if it is my traseu.Intrebarea is ok or should I do the calculation based on the length?
    Thanks in advance.

  12. #12
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Pipe runs

    you may want to insulate the liquid line to prevent (as iceman said) flashing off, is the sight glass clear under load? applies especially if the pipe shaft is warm.

    al

Similar Threads

  1. Mechanical pipe joints
    By davidchesson in forum Fundamentals
    Replies: 7
    Last Post: 18-06-2006, 12:57 PM
  2. pipe sizeing tool
    By Latte in forum Tools and Calculators
    Replies: 5
    Last Post: 10-12-2003, 11:32 PM
  3. Replies: 17
    Last Post: 25-08-2003, 09:56 PM
  4. Pipe sizes
    By benncool in forum Chit Chat & Service Stories
    Replies: 10
    Last Post: 08-07-2003, 10:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •