Results 1 to 18 of 18
  1. #1
    Join Date
    May 2020
    Location
    Uk
    Posts
    22
    Rep Power
    0

    Fitting a failsafe thermal cutout / fuse to a compressor



    Hi all,

    I’ve got an old Prestcold, all restored, rewired and working as well as could be expected.
    The fridge is running from solar in a dry insulated shed but I want to be belt and braces sure that it’s safe should the thermostat fail. (We has a total loss fire at work due to a beko fridge thermostat failing causing the compressor to work overtime until fire broke out).

    My thoughts were to wire a thermal fuse in series from live and mount it onto the compressor, however I have a few stumbling thoughts...

    Firstly, do I wire it into the main circuit effectively killing all power in the event of a blow, or inline with the relay start and run common, therefore just killing power to the compressor circuit?

    Secondly, I can’t for the life of me figure how to mount such a fuse. There are no mount points of any description on top of the compressor, and so I’m stumped. I wondered about magnets but it seems a bit of a ****ty solution for a safety device.

    And lastly, I’m unsure about normal operating temps and so what degree fuse to use?

    I’ll attach some pics of my circuit and the compressor to see if you had any thoughts....

    Thanks

    Chris.
    B1B463C6-3B89-4DB6-A763-87C6A63E2798.jpg
    D5B1EB8F-99D2-4614-AD3C-D85983BF0EAC.jpg



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    Have you looked at "Klixon" safety cutouts?

    Various types and fixings available.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2020
    Location
    Uk
    Posts
    22
    Rep Power
    0

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    I haven’t seen that brand but a quick google search yields similar results to what I’ve seen, I’m struggling with mounting holes on them...

  4. #4
    Join Date
    May 2020
    Location
    Uk
    Posts
    22
    Rep Power
    0

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    I have one of these which operates at 95°C, if I can find a way to mount it to the compressor could I wire it into the black common line to the compressor or is it best to kill all power? The relay is a supco generic start relay, will it continue to try and start and hence get warm if the black common to compressor is interrupted or not?

    Thanks

    Chris

    22B35C80-FA5D-4AFA-9CFE-A7426FB808E1.jpg

  5. #5
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    I can’t see why you need to go to these lengths as old fridges are more robust than modern fridges.
    In the old days I never saw the likes of Prestcold or Frigidaire etc. catch fire.

  6. #6
    Join Date
    May 2020
    Location
    Uk
    Posts
    22
    Rep Power
    0

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    Quote Originally Posted by redroge View Post
    I can’t see why you need to go to these lengths as old fridges are more robust than modern fridges.
    In the old days I never saw the likes of Prestcold or Frigidaire etc. catch fire.
    Up until we had a fire, I’d never seen any fridge catch fire.... I’m fully aware that they are much better constructed than the modern equivalent but in all honesty for a few pounds and a few hours time I’d rather not have the worry of it happening again...

    Don’t mean to be blunt but been there, done that....

    One saving grace is that it is powered by solar, if the compressor was on constantly for a few hours I dare say my battery would be flat long before it had got hot enough to catch, I’m also pretty sure that aside from the very basic wiring insulation there isn’t an awful lot of combustible material present.

    I did wonder about a lower temp cut off, say 50-60 degrees positioned on the back plate behind the compressor, this would obviously then trip if the ambient temp in the immediate area rose....
    Last edited by Allubo; 07-09-2020 at 12:41 PM.

  7. #7
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    .

    A rough guide is if the body is too hot to touch.
    For most people that is the 60 - 70Dec range so 150Dec
    Is extreme.
    That one would be for the discharge pipe of the compressor.
    Get a lower temp one
    https://www.ebay.co.uk/i/17435234793...3d577e93f9b068

    And put it on the body behind the electric box but with good surface contract.

    Rob
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  8. #8
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    .

    Just another thought.

    Check the amp rating and make sure they will take start-up amps

    Rob
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  9. #9
    Join Date
    May 2020
    Location
    Uk
    Posts
    22
    Rep Power
    0

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    Quote Originally Posted by Rob White View Post
    .

    A rough guide is if the body is too hot to touch.
    For most people that is the 60 - 70Dec range so 150Dec
    Is extreme.
    That one would be for the discharge pipe of the compressor.
    Get a lower temp one
    https://www.ebay.co.uk/i/17435234793...3d577e93f9b068

    And put it on the body behind the electric box but with good surface contract.

    Rob
    So you’re saying to mount to the black body panel that sits in front (behind if you were looking at the front of the fridge) of the compressor rather than the compressor itself?

    Thanks

    Chris

  10. #10
    Join Date
    May 2020
    Location
    Uk
    Posts
    22
    Rep Power
    0

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    Or is the best bet to simple wire in a thermal fuse as linked and simply tape it to the top of the compressor?

    https://www.espares.co.uk/product/es...r-thermal-fuse

    Thanks

    Chris

  11. #11
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    Quote Originally Posted by Allubo View Post
    So you’re saying to mount to the black body panel that sits in front (behind if you were looking at the front of the fridge) of the compressor rather than the compressor itself?

    Thanks

    Chris
    It needs to have a good surface contract with the comp body.
    Not too high, maybe 1/3rd up from bottom and the bare electrical connections need protection.
    So behind the box but touching the compressor body. Behind the box is purely for convenience and electrical protection.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  12. #12
    Join Date
    May 2020
    Location
    Uk
    Posts
    22
    Rep Power
    0

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    Quote Originally Posted by Rob White View Post
    It needs to have a good surface contract with the comp body.
    Not too high, maybe 1/3rd up from bottom and the bare electrical connections need protection.
    So behind the box but touching the compressor body. Behind the box is purely for convenience and electrical protection.

    Rob

    .

    Great, I know for sure that start up current will not be more that 2000w momentarily, the fridge is running through a 1000w inverter which has momentary surge of 2000w for starting motors etc so maximum amps it could possibly draw on start up will be around 9amps if I’m not mistaken...?

    Yep I’ll sleeve or otherwise insulate whatever I put there....

    Thanks

    Chris
    Last edited by Allubo; 08-09-2020 at 08:20 PM.

  13. #13
    Join Date
    May 2020
    Location
    Uk
    Posts
    22
    Rep Power
    0

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    Ok so I have a thermal fuse, from what I can tell it’s rated to blow at 72°C and is suitable for a continual load of 10amps upto 250v. So should be perfect. It’s from a beko defrost system and was obviously a readily available part.
    Comes with an epoxy sealed plastic housing so shouldn’t require further insulating.

    Think this will be ok? Installed first into the live cable before going anywhere further into the fridge cabling?

    A06570A9-BE67-48D4-B5D9-1586C8706940.jpg
    26F02C88-3B54-434D-931C-6DEC8FA14756.jpg

    Thanks

    Chris

  14. #14
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    Well it will definitely do the job.

    Regards
    Rob
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  15. #15
    Join Date
    May 2020
    Location
    Uk
    Posts
    22
    Rep Power
    0

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    Thanks, I’ve pulled the cables through some thicker insulation, wired it in and tested operation, just got a 50mm wide silicone band on order to stretch round the compressor with the fuse on the inside to hold it in place.
    The band obviously doesn’t conduct heat or electricity and is resistant to vibration by default.
    Should hold the fuse snugly to the compressor...
    83479619-BD8F-4630-A614-2D411ECEFF6C.jpg
    507A6AA6-752D-4DFD-991D-5C3FB3311BD7.jpg

    Chris

  16. #16
    Join Date
    May 2020
    Location
    Uk
    Posts
    22
    Rep Power
    0

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    Thanks, I’ve pulled the cables through some thicker insulation, wired it in and tested operation, just got a 50mm wide silicone band on order to stretch round the compressor with the fuse on the inside to hold it in place.
    The band obviously doesn’t conduct heat or electricity and is resistant to vibration by default.
    Should hold the fuse snugly to the compressor...
    83479619-BD8F-4630-A614-2D411ECEFF6C.jpg
    507A6AA6-752D-4DFD-991D-5C3FB3311BD7.jpg

    Chris

  17. #17
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    .

    That looks a nice and tidy job.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  18. #18
    Join Date
    May 2020
    Location
    Uk
    Posts
    22
    Rep Power
    0

    Re: Fitting a failsafe thermal cutout / fuse to a compressor

    Thanks, all finished...

    Thank you all for your help!

    C54FED4B-84CE-451A-847B-063B94B4321A.jpg

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •