    Sizing Kw capacity for known volume of water



    Hello members
    Anyone know how much Kw cooling capacity needed to cool 7m3 total of water volume in an indoor open water basin from 26c to 4c where indoor temp. is 23c.
    Thanks for help.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Sizing Kw capacity for known volume of water

    Do you want to know how much energy it will take to cool it or are you looking to select a refrigeration system to cool it?

    For the latter, you need to decide how quickly (time) it needs to be cooled

  3. #3
    Join Date
    Jun 2008
    Location
    Iraq
    Age
    55
    Posts
    29
    Rep Power
    0

    Re: Sizing Kw capacity for known volume of water

    Quote Originally Posted by frank View Post
    Do you want to know how much energy it will take to cool it or are you looking to select a refrigeration system to cool it?

    For the latter, you need to decide how quickly (time) it needs to be cooled
    Thank you Frank. Good question, I wanted to add the time but I ignored it because the basin will used for therapeutic purposes, so there will not be too much change of load on water. Yes I am looking to select a refrigeration system ( a chiller with heat exchanger) to cool the water. The time required to cool is 2-3 Hrs.

  4. #4
    Join Date
    Apr 2020
    Location
    New Zealand
    Posts
    10
    Rep Power
    0

    Re: Sizing Kw capacity for known volume of water

    1 watt 1 litre 1 hour. 7000litres needs 7000watts to move 1 degree in 1 hour. To move 22degrees in 1 hour you need 154kw. Divide the 154kw by 3 to get 52kw.
    Unless you got lots of money, consider a cover and 24hr pull down time.

  5. #5
    Join Date
    Apr 2020
    Location
    New Zealand
    Posts
    10
    Rep Power
    0

    Re: Sizing Kw capacity for known volume of water

    Just so you know. I can definitely sell you a system to do the job, I would need to install and comission.
    Assuming that Iraq still owns their own oil fields, I am picking you've got lots of cash and would be super excited to share Iraqi hospitality with some awesome New Zealanders.

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Sizing Kw capacity for known volume of water

    Seen the news lately?

  7. #7
    Join Date
    Apr 2020
    Location
    New Zealand
    Posts
    10
    Rep Power
    0

    Re: Sizing Kw capacity for known volume of water

    Are you looking for a sweet overseas job Ranger?
    Ya'd have to deal with a couple kiwis.

  8. #8
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Sizing Kw capacity for known volume of water

    Hi
    Q=MC(t2-t1)
    Q= k cal
    M=kg
    t2 = first temperature in C
    t1= our temperature as we want
    Then you divide it in your time as you want .

  9. #9
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Sizing Kw capacity for known volume of water

    Quote Originally Posted by CoolKiwi View Post
    Are you looking for a sweet overseas job Ranger?
    Ya'd have to deal with a couple kiwis.
    You go ahead, good luck if we don’t hear from you.