    Post 12 y/o multi-split issue



    I have a multi-split (two head) system. Been working fine for 12 years.

    One of the head units is not getting hot or cold. It starts up the compressor ok.

    Am I right in thinking this can't be a loss of refrigerant (otherwise both units would fail)?

    I'm an electrician, not an AC guy, so I am wondering if this is something I can fix before I call someone out.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: 12 y/o multi-split issue

    difficult to diagnose on a forum as we would need pressures and temperatures to point us in the right direction.

    it may help if you posted make and model as some brands have inbuilt issues

  3. #3
    Join Date
    Oct 2008
    Location
    New Zealand
    Age
    46
    Posts
    33
    Rep Power
    0

    Re: 12 y/o multi-split issue

    Check the eev coil. Swap the two and see if that fixes the faulty unit.
    More info can be provided if necessary.

  4. #4
    Join Date
    Jun 2020
    Location
    United Kingdom
    Posts
    6
    Rep Power
    0

    Re: 12 y/o multi-split issue

    Do these pictures help?

    AC3.jpg
    AC2.jpg
    AC1.jpg

  5. #5
    Join Date
    Oct 2008
    Location
    New Zealand
    Age
    46
    Posts
    33
    Rep Power
    0

    Re: 12 y/o multi-split issue

    Only manual I can find is an owner's one- tells me nothing.
    The top pipe and 3rd pipe down are the liquid lines. Open cover and trace those pipes till they come to a valve with an electric coil on top, swap those coils over incl where they plug on the PCB.
    Hopefully your unit will start working.

  6. #6
    Join Date
    Jun 2020
    Location
    United Kingdom
    Posts
    6
    Rep Power
    0

    Re: 12 y/o multi-split issue

    Thank you.

  7. #7
    Join Date
    Jun 2020
    Location
    United Kingdom
    Posts
    6
    Rep Power
    0

    Re: 12 y/o multi-split issue

    This thing? How do I take it off. I see a bolt on the front.

    AC4.jpg

    EDIT: Actually, searching for that part, it's coming up as a 4 Way reversing valve. There are two of them. You can just see the other in the background, top right, the other way round.
    Last edited by Tanaka; 02-06-2020 at 09:45 PM.

  8. #8
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: 12 y/o multi-split issue

    Looking at the data plate and the fact you say there are two reversing valves then I'd imagine there are two separate refrigeration circuits. If that's the case and guessing you can't check any pressures then get the faulty circuit only set to run and see if there's any power to the compressor or any pressure switches open circuit for starters.

    Cheers,
    Andy.

  9. #9
    Join Date
    Jun 2020
    Location
    United Kingdom
    Posts
    6
    Rep Power
    0

    Re: 12 y/o multi-split issue

    Yes, two compressors in there. It's dark now. I'll probe about with a meter tomorrow.
    Thanks.

  10. #10
    Join Date
    Oct 2008
    Location
    New Zealand
    Age
    46
    Posts
    33
    Rep Power
    0

    Re: 12 y/o multi-split issue

    Thanks for your input Andy,
    Sounds like someone is going to need some gauges.

  11. #11
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: 12 y/o multi-split issue

    Cheers, they might well need them!

    Not that I've ever seen one in the flesh but a previous job I had at a wholesaler, we had a few calls on similar Fujitsu systems.
    These 2 compressor systems were still dogging on, half in some cases. Typically units with faulty compressors were the ones where you had to take the working one out to get the faulty one out.
    Despite being two completely separate systems the common PCB wouldn't let you use one on heating whilst the other was coming. Shame, a heat recovery split would have been a first!

  12. #12
    Join Date
    Jun 2020
    Location
    United Kingdom
    Posts
    6
    Rep Power
    0

    Re: 12 y/o multi-split issue

    I fixed it.

    Bad capacitor. There were two Toshiba compressors inside. The smaller one fired right up with a new cap.

  13. #13
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 12 y/o multi-split issue

    Glad you've sorted it and thanks for letting us know.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015