    Subcooling Question



    Could anyone answer this question please as I am a bit stumped?
    How can I check the correct saturation temperature for subcooling if my high side gauge is on the liquid line service port just after the expansion device? That won’t give me the correct pressure reading will it?? The unit is an LG UM42. R410a.
    Thanks in advance



  2. #2
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    452
    Rep Power
    17

    Re: Subcooling Question

    There may be another service port for the high side within the outdoor unit. Or there may be a way to get a reading from a pressure transducer, Ive not done much with LG AC so Im not sure.

    A service port after the expansion device wont give the correct pressure for calculating subcooling. But if the unit is reverse cycle for a heating mode you may be able to use that port then.
    Last edited by seanf; 13-04-2020 at 03:01 PM.

  3. #3
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Subcooling Question

    Measure the pipe surface temperature of the condenser mid way through the condenser circuit, this will give you the saturation temperature for the discharge of the system , then measure the pipe temperature at the outlet of the condenser, the temperature difference is the degree of sub cooling . Using a comparator once you have the saturated discharge temperature for R410A then you can work out the discharge pressure. Easy

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Subcooling Question

    You cannot check subcooling at split-system refrigerant charging/evacuation port in cooling mode! You can only check superheat!
    In heating mode, at that point, you can only check total superheat.
    Corect charge is checked by weighing refrigerant.
    Corect operation is checked by measuring air properties!
    For other measurments, you need to install test points and/or use thermal camera and termocouples at apropriate system points to obtain temperature diferences.