    Expansion Check of existing plant



    Dear All,
    We have an existing refrigeration capacity of 1000KW and now we want to upgrade it to 3000KW with addition of similar compressor. Following are the component data for existing components and components being added.
    1- Refrigerant: Ammonia
    2- Required Process cooling water temperature: 0-2C
    3- GEA V1400 compressor 01 existing; Two more compressors to be added.
    4- Condensers: Evaporative condenser 1200KW (wetbulb 28C/conden. Temp 37C/Evaporation Temp: -4C) Same condensers to be added making total 3 condensers
    5- HP receiver size: 500mm x 1200mm vertical (will remain same)
    6- LP Receiver Size: 1200mm x 3500mm horizontal (will remain same)
    7- Expansion Valve: ICS type hand expansion valve (will remain same)
    8- Evaporator: Gravity feed 3000KW PHE (03 meter below LP Rec.)
    9- Ice water tank size is 20000 liters
    10- Piping, we know its OK for pressure drops
    My questions are:
    1- Are HP & LP receivers of sufficient capacity?
    2- How can I check capacity of expansion valve to handle extra flow?
    3- Although evaporator is of 3000KW, will it generate sufficient vapors for working of 3 compressors? How can I check?
    3-Ice water tank capacity is oK or we need to increase its size? What is criteria of its sizing? How to check for its working for peak conditions?
    Regards
    Rize



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Expansion Check of existing plant

    Quote Originally Posted by rize1159 View Post
    Dear All,
    We have an existing refrigeration capacity of 1000KW and now we want to upgrade it to 3000KW with addition of similar compressor. Following are the component data for existing components and components being added.
    1- Refrigerant: Ammonia
    2- Required Process cooling water temperature: 0-2C
    3- GEA V1400 compressor 01 existing; Two more compressors to be added.
    4- Condensers: Evaporative condenser 1200KW (wetbulb 28C/conden. Temp 37C/Evaporation Temp: -4C) Same condensers to be added making total 3 condensers
    5- HP receiver size: 500mm x 1200mm vertical (will remain same)
    6- LP Receiver Size: 1200mm x 3500mm horizontal (will remain same)
    7- Expansion Valve: ICS type hand expansion valve (will remain same)
    8- Evaporator: Gravity feed 3000KW PHE (03 meter below LP Rec.)
    9- Ice water tank size is 20000 liters
    10- Piping, we know its OK for pressure drops
    My questions are:
    1- Are HP & LP receivers of sufficient capacity?
    2- How can I check capacity of expansion valve to handle extra flow?
    3- Although evaporator is of 3000KW, will it generate sufficient vapors for working of 3 compressors? How can I check?
    3-Ice water tank capacity is oK or we need to increase its size? What is criteria of its sizing? How to check for its working for peak conditions?
    Regards
    Rize
    Rize,
    I think you need to hire a refrigeration company to engineer system fully.
    Here are links to some information.

    Danfoss ICS 65
    Reg valve 40B
    https://www.danfoss.com/en/service-a...oolselector-2/

    Vessel might be a bit okay, as see dimmensions
    850tons 3000kw, 1500 diameter x 3250mm HSDD-60-128 20degF

    https://www.johnsoncontrols.com/-/me...FEC3CC9775DBF7

    0 to 2deg water can be dangerous for instant freeze up if power failure.

    Condensers maybe go a bit bigger, as you add motor power input on top of load.
    Also fouling, deterioration of condensers, as well as a pull down if water hotter.
    Last edited by RANGER1; 07-04-2020 at 12:52 PM.

  3. #3
    Join Date
    Feb 2020
    Location
    Pakistan
    Posts
    27
    Rep Power
    0

    Re: Expansion Check of existing plant

    Ranger1, thank you for your valuable input. We have already have a refrigeration company contracted. They say system seems OK. But previously, we have relied on someone with similar words. Now We have getting temperature of 10C to process whenever we have some electrical power changeover. Thats why we are trying to make a check by our-self.
    BTW ice water is a glycol mixture by 10%. so no worries of icing. But what about storage tank volume? 20K liters is enough or we need to add. Tank hot return water is 11C & primary ice water circuit is 2C.
    Our few persons are saying, Condensers are small. They are of opinion that it should be 1600KW as per formula given by RJ Dossat Principals of Refrigeration. (Compressor refrigeration capacity plus motor power multiplied by factor)

  4. #4
    Join Date
    Oct 2016
    Location
    Serbia
    Age
    51
    Posts
    110
    Rep Power
    8

    Re: Expansion Check of existing plant

    I am totally agree with Ranger,If you have reserved with local company that made calculation then you must others worldwide.

    regards
    Aki

  5. #5
    Join Date
    Oct 2016
    Location
    Serbia
    Age
    51
    Posts
    110
    Rep Power
    8

    Re: Expansion Check of existing plant

    And if you go to calculate condenser then you right,compressor capacity,motor power, (capacity of oil cooler),plus factor.

    regards
    Aki