    Thumbs up Attic Heat Pump



    Hello All,

    I'm currently working on a new project: ATTIC HEAT PUMP. The idea is to use refrigerant to pump heat from the attic of my home to a water cooled heat exchanger (condenser). It's an exciting concept; however, the endless little installation details make the project tedious!
    I am using a 2 ton REFRIGERATION UNIT (R22) salvaged from a walk-in cooler. The EVAPORATOR is in the ATTIC, and the CONDENSER is WATER-COOLED (actually GLYCOL - closed loop).
    The GLYCOL LOOP then heats potable water through a second exchanger. I wasn't comfortable running potable water through the used (dirty) condenser.
    ATTIC temperatures are presently rising above 100F! Do I need to run the EVAPORATOR FANS at these very high temperatures?



  2. #2
    Join Date
    Mar 2006
    Location
    Norfolk
    Posts
    160
    Rep Power
    19

    Re: Attic Heat Pump

    Hi Kettler

    You need to get the warm air through the Evap, though I would imagine not quite as quickly as in a cold store.

    I would suggect that you try a smaller and therefore quieter fan unit and take some readings -

    1. No Fan
    2. Normal Fan
    3. Low speed fan

    Perhaps even look at putting a speed controller on the exising fan.

    HTH

    Paula

  3. #3
    Join Date
    Apr 2006
    Location
    USA
    Age
    65
    Posts
    34
    Rep Power
    0

    Smile Re: Attic Heat Pump

    Thanks Paula,

    I was hoping not to need the FANs because they're going to require FILTERs to keep dust from building up inside the EVAPORATOR. Another one of those little time-consuming details I mentioned.

    KETTLER

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Attic Heat Pump

    Quote Originally Posted by KETTLER
    I was hoping not to need the FANs because they're going to require FILTERs to keep dust from building up inside the EVAPORATOR.
    So how do you propose getting the heat transferred from the attic into the evaporator?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: Attic Heat Pump

    adding fan and filter is not a diificult task which is normal for home use air conditioner. Air cooled evaporator is low efficient without forced air through it.
    I hear...I forget;I see...I remember;I do...I understand

  6. #6
    Join Date
    Apr 2006
    Location
    USA
    Age
    65
    Posts
    34
    Rep Power
    0

    Re: Attic Heat Pump

    The attic is so hot, 120F +, that I believe the gas will flash-off once it hits the EVAPORATOR.

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Attic Heat Pump

    OK, so the gas will flash off at that temperature but, and again but, how are you planning to get the heat transfer from the attic to the gas inside the pipes.

    Are you making a contact plate for the pipes to be fixed onto in an attempt at conduction heat transfer?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Attic Heat Pump

    Simple solution ; run system without fan for a few days ,then put a portable fan for forced air and measure the difference

  9. #9
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    20

    Re: Attic Heat Pump

    Also {just in case this is to be overlooked} suggest you get a drip tray under the evaporator, and run a condensate line to waste somewhere, to avoid a wet ceiling or two.

  10. #10
    montreal's Avatar
    montreal Guest

    Re: Attic Heat Pump

    Quote Originally Posted by KETTLER View Post
    The attic is so hot, 120F +, that I believe the gas will flash-off once it hits the EVAPORATOR.
    I am working on a different project which also faces unique challenges.

    If your goal is to extract as much heat as possible with the evaporator that you have, then you will realize that your arrangement will generate a lot of superheat and that will transfer less heat compared to a situation where you can manage to keep your superheat relatively low.

    You can lower the superheat by not overloading your evaporator with heat or by increasing the amount of ***** you are prepared to send to the evaporator.

    You can reduce the overloading on the evaporator by slowing down your attic fan or you can increase the ***** flow without overloading your compressor if you can place your condensor where it is exposed to cold water.

    What I have read is that a small compressor which has its evaporator and condensor coils replaced with coils designed for a larger compressor will allow that smaller compressor to transfer much more energy.

    The fact that your condensor is going to be sunk in water and the fact that your attic is a strong source of heat, together are the equivalent of having larger coils, so your compressor is going to end up moving a lot more heat per hour than it ever did in that walk-in cooler installation.

    Do you plan on having a TEV on your evaporator? If so, you may need to recalibrate it or buy one that lets you play with the set screws. If not, you may be able to simulate the missing TEV by getting your fan to run at a variable speed as a function of the temperature measured on your evaporator's outlet.

    Getting a fan that is rated for a hostile environment (hot) might be a problem. If it is a shaded pole or PSC type motor, then an inexpensive fan motor speed control (dimmer) might be a good idea. You need to get that fan speed controlled by a thermistor attached to your suction line at the evaporator. That calls for approaching someone who knows some electronics.

    There are thermistors that increase in resistance with temperature. Using the thermistor, you need to turn on a small lightbulb (like found in the ceiling light of a car). This light falls on a CDS photocell which has a resistance proportional to the amount of light. The CDS photocell is used to replace the reostat in the fan speed control (dimmer).

    As the superheat goes up, the resistance of the thermistor goes up and the power to the lightbulb goes down and the light output falls and the resistance in the photocell goes up and the speed of the fan goes down so less heat goes into the evaporator and the superheat begins to fall and eventually you have an equilibrium.

    Getting the right amount of light from the bulb for a given temperature calls for a small DC amplifier between the thermistor and the lightbulb with a gain control on the amp that allows you to set the calibration for the right amount of superheat.

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Attic Heat Pump

    Kettlers last activity on this forum wan on 24 June 2006, I think he took some of teh iedeas and is still busy with it.
    Thanks for the help Kettler and for the helpfull info afterwards.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    montreal's Avatar
    montreal Guest

    Re: Attic Heat Pump

    Quote Originally Posted by Peter_1 View Post
    Kettlers last activity on this forum wan on 24 June 2006, I think he took some of teh iedeas and is still busy with it.
    Thanks for the help Kettler and for the helpfull info afterwards.
    I hope he is subscribed to this thread. That way he will receive an e-mail notification and come back and read my information. I will send him a personal message if possible.

    Because it is now nearly winter, he may not be as interested in his project right now.

  13. #13
    Join Date
    Apr 2006
    Location
    USA
    Age
    65
    Posts
    34
    Rep Power
    0

    Re: Attic Heat Pump

    Thank you for your reply! Very informative.

    I'm thinking that the refrigerant will pick up plenty of heat energy as it flashes-off in the attic evaporator and therefore will not need fans.

    This heat energy will be transferrred to a water cooled condenser and used to preheat potable water.


    Thoughts?

  14. #14
    montreal's Avatar
    montreal Guest

    Re: Attic Heat Pump

    Quote Originally Posted by KETTLER View Post
    I'm thinking that the refrigerant will pick up plenty of heat energy as it flashes-off in the attic evaporator and therefore will not need fans.
    I keep forgetting that you are pumping heat from a hot spot to a cold spot, which is in the opposite direction to the way heat is usually pumped either in winter using a heat pump or in summer using an air conditioner.

    If you supply too little heat to your evaporator, you risk flooding your compressor. If you supply too much heat, then your compressor will have to struggle with a large quantity of superheated gas to be compressed.

    If your condensor is kept cool by the water, then the compressor will not have to work that hard. But as your water begins to heat up, then the compressor is going to work against a greater load.

    Perhaps a better solution than the one I originally proposed would be to monitor the amps drawn by the compressor and use this measurement to vary the speed of the evaporator fan so that you keep the compressor running under a constant load.

    Once the water temperature in the reservoir reaches the desired temperature, then you could shutdown the compressor and evaporator fan until the next cycle.

  15. #15
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Attic Heat Pump

    Quote Originally Posted by KETTLER View Post
    The attic is so hot, 120F +, that I believe the gas will flash-off once it hits the EVAPORATOR.
    Why not duct the air and air condition you living space.

    taz

  16. #16
    Join Date
    Apr 2006
    Location
    USA
    Age
    65
    Posts
    34
    Rep Power
    0

    Re: Attic Heat Pump

    Quote Originally Posted by montreal View Post
    Perhaps a better solution than the one I originally proposed would be to monitor the amps drawn by the compressor and use this measurement to vary the speed of the evaporator fan so that you keep the compressor running under a constant load.

    Once the water temperature in the reservoir reaches the desired temperature, then you could shutdown the compressor and evaporator fan until the next cycle.

    Wow! What a terrific idea. Thanks!

  17. #17
    Join Date
    Apr 2006
    Location
    USA
    Age
    65
    Posts
    34
    Rep Power
    0

    Re: Attic Heat Pump

    Quote Originally Posted by taz24 View Post
    Why not duct the air and air condition you living space.

    taz
    There's a lot more energy to heat water in the attic.

    Than ks,
    KETTLER

  18. #18
    Join Date
    Apr 2006
    Location
    USA
    Age
    65
    Posts
    34
    Rep Power
    0

    Re: Attic Heat Pump

    Quote Originally Posted by montreal View Post
    If you supply too little heat to your evaporator, you risk flooding your compressor. If you supply too much heat, then your compressor will have to struggle with a large quantity of superheated gas to be compressed.

    Perhaps a better solution than the one I originally proposed would be to monitor the amps drawn by the compressor and use this measurement to vary the speed of the evaporator fan so that you keep the compressor running under a constant load.
    Perhaps a pressure switch to cycle the fans could be used to govern the load on the compressor?


    KETTLER

  19. #19
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Attic Heat Pump

    Get a voltage controlled oscillator Use a thermistor to sent it a varying voltage based on monitoring point of your choice. Sent the signal to a power fet and connect to the ground side of a dc fan. Now you have a temp speed modulated fan. You can make a VCO out of a 555.

  20. #20
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Attic Heat Pump

    As I understand it, you are going to use a refrigeration system to transfer heat from the attic air to a glycol loop and then pump the heated glycol through a water heater.

    Why not eliminate the refrigeration system and simply pump the glycol through a coil in the attic? It would be far more efficient.

  21. #21
    Join Date
    Apr 2006
    Location
    USA
    Age
    65
    Posts
    34
    Rep Power
    0

    Re: Attic Heat Pump

    Quote Originally Posted by Gary View Post
    Why not eliminate the refrigeration system and simply pump the glycol through a coil in the attic? It would be far more efficient.
    Gary,

    I believe the R22 refrigerant will absorb more heat energy.

  22. #22
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Attic Heat Pump

    Quote Originally Posted by KETTLER View Post
    Gary,

    I believe the R22 refrigerant will absorb more heat energy.
    Ok what is the specific heat capacity per kG off R22, much less that water you will find

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  23. #23
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: Attic Heat Pump

    Kettler
    a system has been available in the UK since the early eighties but has never taken off. The only reason for using refrigerant is to get the required water temperatures required to elliminate the chances of legionella growing, however this can be done using an electric heating element set to boost the temperature above 60degC once a week. This method is used on comercially available heatpump systems.

    Ian

  24. #24
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Attic Heat Pump

    Quote Originally Posted by KETTLER View Post
    Gary,

    I believe the R22 refrigerant will absorb more heat energy.
    You believe transferring heat from air to refrigerant to water is more efficient than transferring heat from air to water?

    Air>Refrigerant>Water

    VS

    Air>Water

  25. #25
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: Attic Heat Pump

    Gary
    I agree with you that air to water would be more efficient however you will struggle to reach the required temperatures for houshold water taking that most of the world take water at 55 def C then mix it with cold water to wash their hands.

    Ian

  26. #26
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: Attic Heat Pump

    good point that considering @ 55 deg C water would burn most people

  27. #27
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Attic Heat Pump

    Here's a better way: Assuming you are in an area that isn't going to freeze the attic, run the supply water through a fan/coil unit in the attic and then down to the water heater. This will preheat the water before it enters the water heater.

  28. #28
    Join Date
    Apr 2006
    Location
    USA
    Age
    65
    Posts
    34
    Rep Power
    0

    Re: Attic Heat Pump

    Thanks Gary,

    I live in the Northeast and freezing is a problem. Also, the water would have to be pumped 20+ feet vertically which would be a significant electrical cost compared to the energy payback.

    I think refrigerant is the way to go because it effectively gathers enthalpy even at low temperatures.


    KETTLER

  29. #29
    Join Date
    Apr 2006
    Location
    USA
    Age
    65
    Posts
    34
    Rep Power
    0

    Re: Attic Heat Pump

    Quote Originally Posted by Andy View Post
    Ok what is the specific heat capacity per kG off R22, much less that water you will find
    Andy,

    Yes, I agree, water does have a greater heat capacity; however, R22 will absorb heat more readily and at lower temperatures. I can collect heat energy at temperatures just above 40F using R22 whereas the well water comes from the ground at 56F.


    KETTLER

  30. #30
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Attic Heat Pump

    Quote Originally Posted by Gary View Post
    As I understand it, you are going to use a refrigeration system to transfer heat from the attic air to a glycol loop and then pump the heated glycol through a water heater.

    Why not eliminate the refrigeration system and simply pump the glycol through a coil in the attic? It would be far more efficient.
    Some one has had a swimming pool heater on the market like that. A fan coil grabs heat from the attic to heat a pool.

  31. #31
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

  32. #32
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Attic Heat Pump

    Quote Originally Posted by Pooh View Post
    Gary
    I agree with you that air to water would be more efficient however you will struggle to reach the required temperatures for houshold water taking that most of the world take water at 55 def C then mix it with cold water to wash their hands.

    Ian
    I don't think we want to run the head pressure that high anyway, so we are talking preheater here.

    The question then is whether it is more efficient to use mechanical refrigeration to heat a preheater heat exchanger...

    or...

    to pump glycol through a fan/coil in the attic to heat a preheater heat exchanger.

    We can move more heat with the refrigeration system, but is it worth it?

  33. #33
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Attic Heat Pump

    Quote Originally Posted by KETTLER View Post
    Andy,

    Yes, I agree, water does have a greater heat capacity; however, R22 will absorb heat more readily and at lower temperatures. I can collect heat energy at temperatures just above 40F using R22 whereas the well water comes from the ground at 56F.


    KETTLER
    We don't want to chill the attic below room temperature or we are fighting the house heating system. And we need to think about condensation. This would be much easier to handle with a fan/coil unit than bare pipes with no fan.
    Last edited by Gary; 28-02-2007 at 03:46 PM.

  34. #34
    Join Date
    Apr 2006
    Location
    USA
    Age
    65
    Posts
    34
    Rep Power
    0

    Re: Attic Heat Pump

    Gary,

    Yes, I agree with you about the evaporator fans - they should be used for greater heat transfer. The condensation will be piped outside.

    I'm not concerned about the heating loss because most of the preheating will take place in the summer when I don't want to run my boiler (especialy to heat water).


    KETTLER

  35. #35
    Join Date
    Mar 2007
    Location
    South Africa
    Posts
    228
    Rep Power
    18

    Re: Attic Heat Pump

    Quote Originally Posted by Andy View Post
    Ok what is the specific heat capacity per kG off R22, much less that water you will find
    Don't forget the latent heat. R22 boils and absorbs latent heat whereas the glycol is purely sensible heat.

  36. #36
    Join Date
    Jan 2008
    Location
    USA
    Posts
    16
    Rep Power
    0

    Re: Attic Heat Pump

    if you (or anyone else) needs a variable speed fan EBM makes a nice reverse impeller type, 0-10vdc control. available in various cfms & pressure drops with ball bearings. very efficient & readily available on ebay.
    ------------------
    saving money on utilites in odd ways ways is cool
    (or warm)
    best;
    eddc

Similar Threads

  1. New Heat Pump Forum
    By Argus in forum Heat Pumps
    Replies: 17
    Last Post: 10-04-2010, 09:12 AM
  2. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  3. Replies: 8
    Last Post: 24-02-2007, 05:17 PM
  4. Rebuild air2air heat pump
    By stalker in forum Technical Speculations
    Replies: 3
    Last Post: 02-11-2006, 10:10 AM
  5. heat pump capacity adjust
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 14-02-2006, 07:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •