    climaventa chiller unit high pressure alarm



    hello

    I have problem with my ac chiller with my hardware board Same as photo my controller is W3000 controller..

    my problem is i have alarm code 211 and 212 is high pressure in circuit 1 and 2,every things in my unit is ok and i check my high pressure is ok and change it by new but still alarm is appear and i connot run compressor.

    we I try to change compete hardware board by new no alarm coming because is new board.SO COULD any one help my to to delete this alarm i have now 10 PCB board with same alarm..!!

    i have user psassoword is 1234
    assitance is 9990
    manfactor is 0000009982

    also i need super user password ??? can any one give me ???



  2. #2
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

    Re: climaventa chiller unit high pressure alarm


  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: climaventa chiller unit high pressure alarm

    Have you reset the trip on the High Pressure switch?

  4. #4
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

    Re: climaventa chiller unit high pressure alarm

    Quote Originally Posted by frank View Post
    Have you reset the trip on the High Pressure switch?
    No reset switch in pressure switch.. Im sure i dont have any problem in pressure switch

  5. #5
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: climaventa chiller unit high pressure alarm

    Have you a photo of hp switches

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: climaventa chiller unit high pressure alarm

    Try the following.
    10 ALARMSPress the ALARM key once to enter the “alarms menu” and view the alarm message along with its code.If there is more than one alarm, scroll the menu using the “Up” and “Down” keys.To reset the alarm, press the ALARM key again and HOLD IT DOWN until “No alarm active” is displayed.If the message does not appear it means that one or more alarm conditions are still active.Press any other key to exit from this menu.
    Good Luck Grizzly
    Despite the High Cost of Living it still remains Popular!

  7. #7
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

    Re: climaventa chiller unit high pressure alarm

    Quote Originally Posted by Grizzly View Post
    Try the following.
    10 ALARMSPress the ALARM key once to enter the “alarms menu” and view the alarm message along with its code.If there is more than one alarm, scroll the menu using the “Up” and “Down” keys.To reset the alarm, press the ALARM key again and HOLD IT DOWN until “No alarm active” is displayed.If the message does not appear it means that one or more alarm conditions are still active.Press any other key to exit from this menu.
    Good Luck Grizzly

    When i tried to press alarm key for 3 second the alarm of high pressure is disappeared but is coming agine after few second.

    Every time i have same alarm I just change the complete PCB hardware and every things working good thats means I dont have any problem in my pressure switch.

    Around 5 years Im changing around 10 PCB when i have same alarm because i dont have another choose..

  8. #8
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

    Re: climaventa chiller unit high pressure alarm

    Even When I tried to make pay pass for high pressure switch by installed wire jumber but still the alarm appeared..

  9. #9
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: climaventa chiller unit high pressure alarm

    Is there a second high pressure switch on the circuit that you are missing? Is the motor thermistor in series with this alarm or any other switch?
    Mostly found in the southern part of this green and pleasant land.

  10. #10
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: climaventa chiller unit high pressure alarm

    Like al said you could have a hp transducer and a Manual reset hp switch it’s not uncommon on some makes of chillers

  11. #11
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

  12. #12
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: climaventa chiller unit high pressure alarm

    Are the pressure transducers 2 wire or 3 wire?

  13. #13
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: climaventa chiller unit high pressure alarm

    Press the black button in the middle of the switch that’s the reset

  14. #14
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

    Re: climaventa chiller unit high pressure alarm

    Quote Originally Posted by frank View Post
    Are the pressure transducers 2 wire or 3 wire?
    2 wire only .. I tried to make wire jumber to paypass but still same alarm ..

    As I say before I dont want to change complete board it is so expensive

  15. #15
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

    Re: climaventa chiller unit high pressure alarm

    Quote Originally Posted by redroge View Post
    Press the black button in the middle of the switch that’s the reset
    I tried and no things happen

  16. #16
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: climaventa chiller unit high pressure alarm

    After pressing the black button you must do what Grizzly said

  17. #17
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: climaventa chiller unit high pressure alarm

    Do you have continuity through the 2 wires from the sensor?

    Disconnect it from the pcb and measure for continuity with a multimeter - even when pressing the reset button.

  18. #18
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

    Re: climaventa chiller unit high pressure alarm

    Quote Originally Posted by frank View Post
    Do you have continuity through the 2 wires from the sensor?

    Disconnect it from the pcb and measure for continuity with a multimeter - even when pressing the reset button.
    Yes I have continuity between 2 wire ( 0.6 ohm) thats means is Normal close

  19. #19
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

    Re: climaventa chiller unit high pressure alarm

    All HP switch has been changed by new but still same alarm . I tried today to change complete board PCB and alram is going .. thats mean I dont have any problem in my unit only in PCB and now I have 11 PCB with same alarm .

    I think there is some software problem may be

  20. #20
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

    Re: climaventa chiller unit high pressure alarm

    Quote Originally Posted by Grizzly View Post
    Try the following.
    10 ALARMSPress the ALARM key once to enter the “alarms menu” and view the alarm message along with its code.If there is more than one alarm, scroll the menu using the “Up” and “Down” keys.To reset the alarm, press the ALARM key again and HOLD IT DOWN until “No alarm active” is displayed.If the message does not appear it means that one or more alarm conditions are still active.Press any other key to exit from this menu.
    Good Luck Grizzly
    When the alarm is appear I press alarm key button for 5 second and alarm is disappeared but after few second alarm is comming back again.
    I Cant run any compressor because this alarm

  21. #21
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: climaventa chiller unit high pressure alarm

    If you link out the HP switch does your chiller run?

  22. #22
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: climaventa chiller unit high pressure alarm

    Have you got a photo of the wiring diagram

  23. #23
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

    Re: climaventa chiller unit high pressure alarm

    Quote Originally Posted by frank View Post
    If you link out the HP switch does your chiller run?
    No Not running

  24. #24
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

    Re: climaventa chiller unit high pressure alarm

    Quote Originally Posted by redroge View Post
    Have you got a photo of the wiring diagram
    I dont have any wiring dirgram

  25. #25
    Join Date
    Mar 2020
    Location
    Poland
    Posts
    1
    Rep Power
    0

    Post Re: climaventa chiller unit high pressure alarm

    Quote Originally Posted by Munther View Post
    I dont have any wiring dirgram
    https://www.manualslib.com/manual/49...page=30#manual


    Here is the manual, there is a description of the board and connections. Also check the factory settings - at what pressures HP is etc.

    Maybe it will help.

    [Google translator]

  26. #26
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: climaventa chiller unit high pressure alarm

    What is the Alarm Number on the display?

  27. #27
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: climaventa chiller unit high pressure alarm

    Quote Originally Posted by frank View Post
    What is the Alarm Number on the display?
    Look at his first post, AL:211 circuit 1

  28. #28
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

    Re: climaventa chiller unit high pressure alarm

    Did any body know how to connect my Pc to this PCB
    Which software can I use ?? DCC16C95-256C-4B51-9E0E-B415E126B87B.jpg

  29. #29
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

    Re: climaventa chiller unit high pressure alarm

    Any update ����

  30. #30
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: climaventa chiller unit high pressure alarm

    If you have continuity whole time on control circuit related to that alarm, you should take that board to electronic repair shop and tell them to check digital inlet which is related to that alarm. Probably optocoupler issue!

    If there is no problem with related digital inlet than it is software issue and you should contact dealer of these units!
    Last edited by nike123; 15-07-2020 at 01:20 AM.

  31. #31
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: climaventa chiller unit high pressure alarm

    Quote Originally Posted by Munther View Post
    All HP switch has been changed by new but still same alarm . I tried today to change complete board PCB and alram is going .. thats mean I dont have any problem in my unit only in PCB and now I have 11 PCB with same alarm .

    I think there is some software problem may be
    Are you saying that you have 11 separate chillers with same alarm?

  32. #32
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: climaventa chiller unit high pressure alarm

    Had a similar problem turned out to be the battery module which feeds the alarm relays if memory serves me right. Caused by low battery voltage but for some reason gives up hp fault.
    Gibbo
    Last edited by Gibbo; 15-07-2020 at 03:42 PM.

  33. #33
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

    Re: climaventa chiller unit high pressure alarm

    Quote Originally Posted by nike123 View Post
    Are you saying that you have 11 separate chillers with same alarm?
    yes I have around 11 PCB with same alarm . there is any software can i connect my board to my lab top and reprogramming the PCB. because Im sure no hardware problem .

  34. #34
    Join Date
    Feb 2020
    Location
    Oman
    Posts
    17
    Rep Power
    0

    Re: climaventa chiller unit high pressure alarm

    did any boady have any idea how to connect my PCB of chiller to my PC ? there is any software can i use it?

  35. #35
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: climaventa chiller unit high pressure alarm

    https://www.carel.com/programming-to...KK/10191/54942
    https://www.carel.com/product/c-suite


    But you probably dont have acess to change programing off these PCO-s since Climavenata is making its own software for PCO and it is protected.

    Your best bet is to contact manufacturer.

    By my expirience, they will never admit that their software is faulty and you will be bounced around like some stupid monkey folowing their instructions. But, maybe you will be lucky monkey!

    I usualy install μchiller2 SE in that case, if it is possible.
    Last edited by nike123; 23-08-2020 at 10:27 AM.

  36. #36
    Join Date
    Apr 2011
    Location
    Russia
    Age
    51
    Posts
    139
    Rep Power
    16

    Re: climaventa chiller unit high pressure alarm

    Are you sure that High pressure alarm comes from HP switch but not HP sensor?