    unbalance current



    Dear Sirs,

    Is it normal to measure current on Motor grounding cable IF no can this cause unbalance current.
    Please be informed we have two motor one by inverter and the other one by soft-starter and they have the same problem (unbalance current)
    grounding system TNC

    looking forward to read from you
    Thank you



  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: unbalance current

    Hi
    Unbalanceing current can be from .

    Unequal of voltage
    Unequal of ohm's in Electromotor
    Leak or damaging wiring in electromotor
    Loose wire in connection box or wiring system
    Test electromotore with megger and leak of that

    Don't worry for
    2 of 3 percent unbalancing with equal voltage .

  3. #3
    Join Date
    Feb 2012
    Location
    libya
    Age
    41
    Posts
    94
    Rep Power
    13

    Re: unbalance current

    thank you mbc
    the current unbalance more than 10% and nothing from the above

  4. #4
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: unbalance current

    Hi
    Also if you have broken conduction on ROTORS Your current always move and come down and goes up .

  5. #5
    Join Date
    Feb 2012
    Location
    libya
    Age
    41
    Posts
    94
    Rep Power
    13

    Re: unbalance current

    this is an ammonia plant with two stage each stage with separate electrical panel but both of them supply from same transformer the current unbalance occur only in one stage and we notice this unbalance for all the motor compressors and pumps

  6. #6
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: unbalance current

    Check your voltages phase to phase not phase to earth or neutral sounds like could be low voltage on supply voltage

  7. #7
    Join Date
    Feb 2012
    Location
    libya
    Age
    41
    Posts
    94
    Rep Power
    13

    Re: unbalance current

    The source voltage phase to phase as following:
    V1=380.1 v
    V2=383.2 v
    V3=377.9 v

    The load voltage phase to phase as following:
    V1=372.1 v
    V2=380.3 v
    V3=374.3 v

    The source power feeds the load through 6 single core 300mm2

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: unbalance current

    Erm!
    Sorry for being silly!
    But What exactly is your problem with the plant?
    Only that's not 10% error
    Does your plant not operate properly or are you just worried about what you are seeing\/
    Last edited by Grizzly; 03-10-2019 at 09:50 AM.
    Despite the High Cost of Living it still remains Popular!

  9. #9
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: unbalance current

    The way invertors are grounded can cause many problems . Also the type of invertor can cause current issues. The size of the earth bonding cable and its route from the motor to the invertor etc all can cause problems . Is the invertor sensing a current problem and alarming or is this just an observation
    What are the current readings at the motor terminals as the safeties in the invertor and the soft starter should detect any problem and log any errorp

  10. #10
    Join Date
    Feb 2012
    Location
    libya
    Age
    41
    Posts
    94
    Rep Power
    13

    Re: unbalance current

    The two screw compressors driven by the same invertor type SINAMICS G130 one of them has current unbalance and the other no
    please see attached motors readings
    cp1 Percentage Imbalance: 9.3% (invertor )
    cp2 Percentage Imbalance: 14.1% (Soft starter)
    cp3 Percentage Imbalance: 2.3% (invertor)
    cp4 Percentage Imbalance: 2.2% (Soft starter)

    cp1 and cp2 MP, also the pump connected to this panel has current unbalance
    cp3 and cp4 LP
    Attached Images Attached Images

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: unbalance current

    Inverter powered motors and soft starters always have current on motor grounding cable because of inverter filtering circuit.
    What I would suggest is call energy distribution company specialist to check distribution panel and cables since unbalance is common factor on one distribution panel.

  12. #12
    Join Date
    Feb 2012
    Location
    libya
    Age
    41
    Posts
    94
    Rep Power
    13

    Re: unbalance current

    we are still troubleshooting and i am sure you will help me gentlemen and now are thinking of the electro- magnetic fields which generated by single core cables but we are wondering why only this panel, the other one ok and they are from the same transformer the same main distribution panel

    Thank you