    Advise about pipe connection for air cooler



    Hello my friends
    Please Advise about pipe connection for air cooler. when i checked R22 plant this problem Drew attention the air cooler connection i know there are cooler top feed type and other bottom feed . this air cooler use in freezing system -25C by over feed pumped liquid. here in attach pic. see top feed but i prefere to modifiy to change to bottom feed FYI the top header is 3 inch and low header is 2 1/2 inch.
    thank for all
    Attached Images Attached Images



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Advise about pipe connection for air cooler

    what material is the pipe made of?

  3. #3
    Join Date
    Mar 2007
    Location
    Egypt
    Age
    55
    Posts
    54
    Rep Power
    18

    Re: Advise about pipe connection for air cooler

    Quote Originally Posted by chemi-cool View Post
    what material is the pipe made of?
    Coil of cooler material is galvanize and connection pipes steel

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Advise about pipe connection for air cooler

    What pressure and temp at the connection point? Are there any vibrations at any of the sides?

  5. #5
    Join Date
    Mar 2007
    Location
    Egypt
    Age
    55
    Posts
    54
    Rep Power
    18

    Re: Advise about pipe connection for air cooler

    Quote Originally Posted by chemi-cool View Post
    What pressure and temp at the connection point? Are there any vibrations at any of the sides?
    the pressure and temp. are not available at these point but I think that when the coil is completely full with pumped liquid the gas resulting from evaporation and goes up against the liquid hole happening decrease in ΔP. this make liquid stop and when the ΔP increase again liquid flow will start again IS MY THINKING OK OR NO ?

  6. #6
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Advise about pipe connection for air cooler

    Quote Originally Posted by dolce View Post
    the pressure and temp. are not available at these point but I think that when the coil is completely full with pumped liquid the gas resulting from evaporation and goes up against the liquid hole happening decrease in ΔP. this make liquid stop and when the ΔP increase again liquid flow will start again IS MY THINKING OK OR NO ?
    If hand expansion valve open to much, or if has suction riser full of liquid unit will not work as well in either situation, top or bottom feed.
    Why do you think you have to change it?
    What type of defrost method do you have, hot gas, water?

  7. #7
    Join Date
    Mar 2007
    Location
    Egypt
    Age
    55
    Posts
    54
    Rep Power
    18

    Re: Advise about pipe connection for air cooler

    Quote Originally Posted by RANGER1 View Post
    If hand expansion valve open to much, or if has suction riser full of liquid unit will not work as well in either situation, top or bottom feed.
    Why do you think you have to change it?
    What type of defrost method do you have, hot gas, water?
    Dear RANGER
    the suction line without riser and oil trap. this cooler is feeded by overfeed method and hot gas method as mentioned below Untitled.png

  8. #8
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Advise about pipe connection for air cooler

    Hi, dolce..

    Quote Originally Posted by dolce View Post
    Hello my friends
    Please Advise about pipe connection for air cooler. when i checked R22 plant this problem Drew attention the air cooler connection i know there are cooler top feed type and other bottom feed . this air cooler use in freezing system -25C by over feed pumped liquid. here in attach pic. see top feed but i prefere to modifiy to change to bottom feed FYI the top header is 3 inch and low header is 2 1/2 inch.
    thank for all
    According to attached photo your evaporator is designed for bottom feeding (header is 2 1/2") and top one is 3" .. I do not see any problem to connect evaporator as you mentioned ... Seems your defrosting cycle will be completely manual ... or maybe attached scheme is not complete because there are lot of valves missing, but if all is new you have a lot of possibilities how to solve complete connection of the evaporator to the system.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  9. #9
    Join Date
    Mar 2007
    Location
    Egypt
    Age
    55
    Posts
    54
    Rep Power
    18

    Re: Advise about pipe connection for air cooler

    Quote Originally Posted by Josip View Post
    Hi, dolce..



    According to attached photo your evaporator is designed for bottom feeding (header is 2 1/2") and top one is 3" .. I do not see any problem to connect evaporator as you mentioned ... Seems your defrosting cycle will be completely manual ... or maybe attached scheme is not complete because there are lot of valves missing, but if all is new you have a lot of possibilities how to solve complete connection of the evaporator to the system.

    Best regards, Josip
    Thank you
    please find attach file and please help me to choose the bestAMMONIA .pdf

  10. #10
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Advise about pipe connection for air cooler

    dolce,
    Sometimes headers have orifice in each circuit of inlet header, so if changing pipework need to check first.

    Top picture is way to go as suction lines independent & free flowing.

    In my first post I asked if something wrong, as your pipework could be totally flooded if regulating valve is open to much causing poor temperatures.

    If inlet & outlet mixed up, of course problems also.

    Pump liquid line also need non return valve after solenoid valve for hot gas defrost, as not shown in schematic.

    Is there enough load on plant other than this to generate enough hot gas to defrost both units at once?
    Last edited by RANGER1; 28-01-2019 at 09:16 PM.

  11. #11
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Advise about pipe connection for air cooler

    Hi, dolce ...

    Quote Originally Posted by dolce View Post
    Thank you
    please find attach file and please help me to choose the bestAMMONIA .pdf
    I agree with RANGER1 suggestion and questions ... we do not know anything about your plant and your idea ... so it is not easy to give you the best advice ...
    instead check attached drawing ... how we did things 20+ years ago ...

    for sure it is not bad idea to use liquid feed regulating valve in front of each cooler ... more expensive, but for sure less headache after ... of course you can use other types of solenoid valves i.e. available to you ...



    Ammonia piping of two coolers in paralell.pdf

    HG - hot gas
    PL - liquid delivery line
    R - return line - suction
    HGR - hot gas return - defrost liquid and gas return

    Hope this will be of some help to you ... anyhow we are here for any further help ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  12. #12
    Join Date
    Mar 2007
    Location
    Egypt
    Age
    55
    Posts
    54
    Rep Power
    18

    Re: Advise about pipe connection for air cooler

    Quote Originally Posted by Josip View Post
    Hi, dolce ...



    I agree with RANGER1 suggestion and questions ... we do not know anything about your plant and your idea ... so it is not easy to give you the best advice ...
    instead check attached drawing ... how we did things 20+ years ago ...

    for sure it is not bad idea to use liquid feed regulating valve in front of each cooler ... more expensive, but for sure less headache after ... of course you can use other types of solenoid valves i.e. available to you ...



    Ammonia piping of two coolers in paralell.pdf

    HG - hot gas
    PL - liquid delivery line
    R - return line - suction
    HGR - hot gas return - defrost liquid and gas return

    Hope this will be of some help to you ... anyhow we are here for any further help ...

    Best regards, Josip
    many thanks and appreciate your reply and help
    i asked only about i think i have problem in connection because this cooler is overfeed type and bottom feed , work by R22 the owner of the plant called me to check the many of problems . i asked the technicians did you charge oil say yes i asked How many oil drums you charge in 6 months answer 6 drums about 1200 Kg i asked did you drain oil out say No and one of wrong thing the cooler was designed to bottom feed and there is not oil riser or oil trap .in defrost process oil can not return .for these i want to modify the connection bottom feed and return oil from small size to main suction line is my idea Ok or not wait your advise .
    yes i completely agree with you in your drawing it is the original design . yes i will modify as your advise
    many thank you
    Last edited by dolce; 30-01-2019 at 05:19 PM.

  13. #13
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Advise about pipe connection for air cooler

    This is the way I would have done it:


    -starting on top with the hotgas, I like to have a bleed valve 1/2 the size of the main line to prevent any hydraulic shock when the defrost starts, usually let it bleed 1 minute before the main defrost opens.

    -Liquid line, you need a non return valve AFTER the liquid solenoid
    I also use an overflow valve (danfoss OFV25) adjusted to open at 5 bar during defrost, sending the liquid back into the main suction line. since you have isolating valves betore and after the suction solenoid valve I elected to connect it between the suction solenoid and the isolating valve for ease of service.

    -Suction line, the bleed valve needs to be across the suction solenoid to bleed the pressure down, unless you want your suction line to do this: after every defrost.

    I'm guessing that the two valves on the liquid line closest to the coolers are reg valves used to balance the liquid feed.
    -Cheers-

    Tycho

  14. #14
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Advise about pipe connection for air cooler

    Quote Originally Posted by dolce View Post
    many thanks and appreciate your reply and help
    i asked only about i think i have problem in connection because this cooler is overfeed type and bottom feed , work by R22 the owner of the plant called me to check the many of problems . i asked the technicians did you charge oil say yes i asked How many oil drums you charge in 6 months answer 6 drums about 1200 Kg i asked did you drain oil out say No and one of wrong thing the cooler was designed to bottom feed and there is not oil riser or oil trap .in defrost process oil can not return .for these i want to modify the connection bottom feed and return oil from small size to main suction line is my idea Ok or not wait your advise .
    many thank you
    An easier way to remove oil from the coolers, is if you connect the OFV line to the bottom line on the cooler and the outlet of the OFV to the highest point on the suction/return line.

    If I remember correctly, you can have 20% of oil mixed in the ***** charge before it starts becomming a problem.


    Is there any type of oil return from the LP receiver to the compressors?


    I would start looking there before I started rebuilding anything
    -Cheers-

    Tycho

  15. #15
    Join Date
    Mar 2007
    Location
    Egypt
    Age
    55
    Posts
    54
    Rep Power
    18

    Re: Advise about pipe connection for air cooler

    Quote Originally Posted by Tycho View Post
    An easier way to remove oil from the coolers, is if you connect the OFV line to the bottom line on the cooler and the outlet of the OFV to the highest point on the suction/return line.

    If I remember correctly, you can have 20% of oil mixed in the ***** charge before it starts becomming a problem.



    Is there any type of oil return from the LP receiver to the compressors?


    I would start looking there before I started rebuilding anything
    Yes Tycho this good idea for me thanks what about for useing Mobile arctic 300 oil with R22?

  16. #16
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Advise about pipe connection for air cooler

    Dolce,
    As you & Tycho mention, system appears heavily oil logged.
    Evaporator full of oil is symptom of oil return from liquid recirculated vessel not returning oil to common still that should be in system.
    If compressors throwing over a lot of oil it may also not be able to keep up with oil return system.
    Can you show how oil return works on pump vessel?
    It sounds so full of oil, best to pump system or components down & drain oil out of system if drain points available.

    Oil probably ok, but seems more suitable for higher temperature applications above -25 deg C

  17. #17
    Join Date
    Mar 2007
    Location
    Egypt
    Age
    55
    Posts
    54
    Rep Power
    18

    Re: Advise about pipe connection for air cooler

    Quote Originally Posted by RANGER1 View Post
    Dolce,
    As you & Tycho mention, system appears heavily oil logged.
    Evaporator full of oil is symptom of oil return from liquid recirculated vessel not returning oil to common still that should be in system.
    If compressors throwing over a lot of oil it may also not be able to keep up with oil return system.
    Can you show how oil return works on pump vessel?
    It sounds so full of oil, best to pump system or components down & drain oil out of system if drain points available.

    Oil probably ok, but seems more suitable for higher temperature applications above -25 deg C
    Ok 222.pdf oil return from taking a small amount of pumped liquid to HP receiver in internal coil making separation and evaporate the liquid , go together to compressor suction as shown mentioned

  18. #18
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Advise about pipe connection for air cooler

    Quote Originally Posted by dolce View Post
    Ok 222.pdf oil return from taking a small amount of pumped liquid to HP receiver in internal coil making separation and evaporate the liquid , go together to compressor suction as shown mentioned
    It looks good, is it working, can you have a sight glass or something to monitor oil return so oil & gas, not liquid returning to compressor which can cause compressor to use oil especially reciprocating compressor.
    What type & how many compressors?
    Are they throwing over excess oil, if so has oil separator oil return working, do they have coalescing filters, have they been replaced, is compressor getting flood backs?
    High pressure liquid receiver would also have to have correct level to warm oil return line. Liquid flood back to compressors could also contribute to oil consumption of compressor.
    Last edited by RANGER1; 31-01-2019 at 04:36 AM.

  19. #19
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Advise about pipe connection for air cooler

    Hi
    As you know the density of oil is a less than R22
    So the oil will stay on top of R22
    to remove that in wet Evaporator system is not easy
    you have to feed hot gas from suction side and let goes to
    return pipe suction line or if you got own line for returning liquid line during defrost system
    give more time for defrost to push R 22 and oil goes for return pipe and it become a little warm
    your system has separator and feed by pump

    All oil goes back to separator and you have to remove it with RECTIFIER VESSEL system


    You need a rectifier vessel with either an electric heater or hot gas
    Last edited by mbc; 31-01-2019 at 04:59 PM.

  20. #20
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Advise about pipe connection for air cooler

    Quote Originally Posted by RANGER1 View Post
    It looks good, is it working, can you have a sight glass or something to monitor oil return so oil & gas, not liquid returning to compressor which can cause compressor to use oil especially reciprocating compressor.
    What type & how many compressors?
    Are they throwing over excess oil, if so has oil separator oil return working, do they have coalescing filters, have they been replaced, is compressor getting flood backs?
    High pressure liquid receiver would also have to have correct level to warm oil return line. Liquid flood back to compressors could also contribute to oil consumption of compressor.
    This, we use a TX valve on the liquid line to measure across the heat exchanger, also a reg valve and a sight glass before compressor suction
    -Cheers-

    Tycho

  21. #21
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: Advise about pipe connection for air cooler

    Some crude drawings of oil rectifier designs, I'm getting pretty good at MS Paint

    oil rectifier.jpg
    This is by far the easiest one to install and adjust.
    One side is fed from the refrigerant pump discharge, through a solenoid (not on drawing) solenoid opens when 1 of the compressors start, liquid is fed through a TX valve into the heat exchanger, on the outlet I always put a Reg valve to adjust the flow during start up (it may be a bit exessive until the TX valve catches up), during normal operation there will be a nice and slow trickle of almost refrigerant free oil.

    Warm side is fed by warm liquid from the HP receiver, doesn't matter if the liquid valve to the LP receiver is on/off or stepless.

    oilrectifier1.jpg

    This one is still fed by the refrigerant pumps, but can be a pain to adjust properly.
    Liquid is fed from the refrigerant pump discharge through a Reg/needle valve (usually 1/2" pipe) into a balancing pipe the balancing pipe drains back to the bottom of the LP receiver.
    The important part is to fill the rectifier to no more than 80%.
    When warm liquid enters on the other side of the tubes, it will cause boiling on the cold side that in turn lifts the "oil rich" refrigerant up to the pipe feeding the compressor suction.

    Reg valve and sight glass on the line to compressor suction is an absolute must

    oilrectifier2.jpg

    Same as the previous one, except this one does not have a balance pipe, the cold side is connected to the LP drum.

    Main issue with this type is that you have to have a pretty stable level in the LP receiver, this type is almost exclusively used on Chillers where you have a very stable/fixed level.


    My favourite is the fist one, because it's easiest to comission, and "it just works"
    -Cheers-

    Tycho

  22. #22
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Advise about pipe connection for air cooler

    Nice drawings & explanations Tycho