    Water pump capacity



    If i have a closed water circuit in a Building with 5 floors.
    Would it require the same water pump capacity if the water pump was placed on the 5. floor Vs 1. floor?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Water pump capacity

    Shouldn't make any difference.

    The pressurisation unit pressure settings will be dependant on its location.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Water pump capacity

    You need pump with greater head.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Water pump capacity

    Quote Originally Posted by Segei View Post
    You need pump with greater head.
    Please explain.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Water pump capacity

    Every centrifugal pump has nominal head and capacity. To provide required capacity for 5th floor, pump should have greater head. Usually, head can be increased by choosing two stages pump. Assume that the lift is 15 meters. It means that nominal head of the pump should be 1.5 bars greater than nominal head of the pump for the first floor.

  6. #6
    Join Date
    Aug 2008
    Location
    Auckland
    Age
    55
    Posts
    264
    Rep Power
    21

    Re: Water pump capacity

    Quote Originally Posted by Segei View Post
    Every centrifugal pump has nominal head and capacity. To provide required capacity for 5th floor, pump should have greater head. Usually, head can be increased by choosing two stages pump. Assume that the lift is 15 meters. It means that nominal head of the pump should be 1.5 bars greater than nominal head of the pump for the first floor.
    But what about the weight/pressure of the returning water? I could be wrong, but what you're describing is pumping water to height with no return path?

  7. #7
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    867
    Rep Power
    26

    Re: Water pump capacity

    It is true that the return will negate the head required to reach a height in a system.
    However you have to get liquid up to a higher point before this works. (Over the hump, so to speak)
    And should you have air or the system is stopped you may not be able to get it going again.

  8. #8
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Water pump capacity

    You are right. I mentioned about open loop system. For closed loop I would be concerned about cavitation on suction side. Pump located on first floor will not have cavitation.