05-06-2006, 07:12 PM #1
Switching device
Hi Friends,
I'm looking for a simple alternate switching device between two split units.
Thanks and Regards
Pravin
-
05-06-2006, 07:15 PM #2
Re: Switching device
Originally Posted by Pravin
What exactly do you want to switch? It is not clear from your question
-
05-06-2006, 11:01 PM #3
Re: Switching device
As easy as it can get. Common is central, one normally open and one normally closed.
-
06-06-2006, 05:47 PM #4
Re: Switching device
Originally Posted by frank
Thanks for your prompt reply & sorry for not being to the point- What i'm actually looking for is a switching module (timer/contactor) that can sequencially switch on and off 2 split type units automatically.
Tks and Regards
Pravin
-
06-06-2006, 05:49 PM #5
Re: Switching device
Originally Posted by NoNickName
Thanks for your prompt reply - What i'm actually looking for is a switching module (timer/contactor) that can automatically and sequencially switch on and off 2 split type units
Tks and Regards
Pravin
-
06-06-2006, 06:25 PM #6
Re: Switching device
Hello parvin
Don't know what is the time duration you wants to switch on and off the units and also dont know how much you can spend on control parts, anyhow you can make it with a motor driven 7day/24hour timer with adj dial type settings and 16 amps 240 volt switch's (if available there), break low voltage control supply at split units p.c or control transformer and you have an automatic hours based change over, also if you need a temperature change over then have to add some more controls as thermostat and additional control relays.
-
06-06-2006, 09:18 PM #7
Re: Switching device
http://www.maplin.co.uk/Module.aspx?...=timer&doy=6m6
Then you can interface the output to a switchover relay.
-
08-06-2006, 01:16 PM #8
Re: Switching device
Originally Posted by malik55
Thank you for your consideration- Well the two units will be in a server room and i need them to work at every 8 hrs sequencially; i.e Unit 1 works from 8 a.m to 16hrs , then from 16 hrs unit 2 takes over up to 24.00hrs. I would rather have a cheap system using single channel timer and a contactor but a schematic diag. of the control you have described would be welcome.
Regards
-
08-06-2006, 01:38 PM #9
Re: Switching device
No problem, Pravin! Contact me and I’ll build you a control panel to switch from one unit to the other automatically with a clock: on a fault of one of the units: or both units switched on if a high temperature condition occurs.
-
08-06-2006, 05:07 PM #10
Re: Switching device
Hello pravin
First say sorry for your name's spellings,
Second I have no scanner to scan a drawing, and I think to draw on the forum is not possible, but anyhow it is not so difficult you have an idea
Walden may help you.Last edited by malik55; 08-06-2006 at 05:15 PM.
Similar Threads
-
Neutrel switching
By wizzer in forum CommercialReplies: 13Last Post: 18-04-2009, 12:18 AM -
Is a capillary tube considered to be a modulating mtering device, as a TXV is.
By TopMechanic in forum FundamentalsReplies: 10Last Post: 20-07-2006, 10:00 PM -
Energy Managment XDX Device
By Steve Wright in forum Supermarket RefrigerationReplies: 1Last Post: 08-09-2005, 06:19 PM -
Metering device?
By Apoc in forum IndustrialReplies: 18Last Post: 20-07-2004, 09:36 AM -
metering device sizing
By dantoubiana in forum Technical SpeculationsReplies: 7Last Post: 21-01-2003, 07:17 PM