    rated v actual



    chaps

    got a swimming pool heat pump which has a tag rating of 45,000 btu . IMG_20171120_092636[1].jpgIMG_20171101_102425[1].jpg no problem

    however the compressor has failed and investigations reveal it's rated at 24,000 btu.

    apart from heat of compression what am I missing?

    pool temp 27c outdoor air averages 25c

    TIA



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: rated v actual

    Somebody was pulling a fast one, who confirms that a piece of ready made kit is working as per specification?

    Install in the summer and get a quick look warm up.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2010
    Location
    devon
    Age
    52
    Posts
    837
    Rep Power
    24

    Re: rated v actual

    Had the same in the summer on a pool heater first time I had looked at it but unit had two new comps in twelve months thought comp looked small at time checked rating plate and approx 2 kws short of data plate spoken to manufacture who advised me there is a 2.5 kw immersion element in the tank to give its output went back fitted comp found element failed got that replaced got total output and a comp that turned off at least we found out why customers electric bill had gone down !

  4. #4
    Join Date
    Aug 2014
    Location
    USA
    Posts
    38
    Rep Power
    0

    Re: rated v actual

    The actual capacity of the compressor in the pool heater application would well be greater than the rated capacity of the compressor if it's rated at air conditioning condensing and evaporator temps. With the 27C/25C water and air, the saturated suction could be as high as 15C and condensing as low as 35C. That would kick it way up, though not double...

    ZR24.jpg

  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,537
    Rep Power
    36

    Re: rated v actual

    .

    45000 btu is about 13kW and input power on
    data plate says it is 2.37kW.

    If that is the case then you has an efficiency rating of
    13/2.37 = 5.4 so that sounds reasonable

    Are you saying that after checking the system is only
    rated at 24000 btu or the comp is rated at 24000 btu?

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..