    So guys, what is the situation in your country regarding the calibration of every temperature recoder installed after 1.1.2006 as defined by EN13486 regulation?

    We're just starting it



  2. #2
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: En13486

    Hi Nova,

    I dont know what MTK have on their ticksheets (Reeferjon should know) but most companies as standard on a 1500hr service will put a probe in the back on the air return and check the calibration.

    Dont know how G & A and Schmitz send their units out but we used to have to check the calibration on 3 things. Stat, Box gauge and recorder.

    All we used to do was run the unit to 0 and write temps on the back of the ticksheet and obviously make adjustments as necc. If there is new legislation coming in then the must be more paperwork involved just to give someone in Brussells something to do

    Regards

    Fatboy

  3. #3
    Join Date
    Nov 2001
    Location
    Shropshire
    Age
    59
    Posts
    260
    Rep Power
    23

    Re: En13486

    Took a peek at the BS site today...EN13486 is still dated 2002 EN12830 is still 1999.

    Have you got a link to your data that calls for a change in 2006.

    Thanks.
    John.