Thread: need energy consumption data
24-05-2006, 10:05 PM #1
Hi everybody,
I am planning a cold-storage room(about 30 m2) to cool 10thousands of jars of jam from 70C to 25C in 60 minutes. I have calculated the total heat removal as 70.52 kW. Can you give an average electricity consumption of a typical cooler to provide this heat removal?
There will also be fans to blow air at 20m/s. But i can calculate that seperately.
Thanks...
24-05-2006, 10:53 PM #2
Re: need energy consumption data
70kW would require approx 20.000 m3/h, that is 200 volumes per hour. Such blowers would consume 2 to 3 kW for an average blower with axial fans.
The power consumption for the chiller or condensing unit depends on the selected evaporating temperatures, I would say around 8-12°C, which would result to a COP of around 4.
As such, the power consumption for the compressor will be approx 18-19kW.
Less if a chiller is used.
25-05-2006, 12:48 AM #3
Hello gokhan,
Welcome to the RE website.
I have some comments about your question below.
The refrigeration system will use more energy if the evaporating temperature is 5C, rather than 20C. You did not mention how low the final temperature would be.
At the same time, if you use air-cooled condensing the energy cost and use will increase. If a water cooled condenser is used, the energy use will be reduced.
10,000 jars is a lot of jam!
Helpful information
By chemi-cool in forum Tools and CalculatorsReplies: 2Last Post: 30-10-2010, 07:00 PM -
Energy Conservation
By US Iceman in forum Technical SpeculationsReplies: 20Last Post: 20-07-2010, 10:52 AM -
Very High Energy Consumption
By gdiaz in forum Trouble ShootingReplies: 12Last Post: 17-01-2007, 03:56 PM -
A question about energy efficiency rating in Europe
By pcdata76 in forum FundamentalsReplies: 1Last Post: 22-05-2006, 10:17 AM -
Direct Energy Consumption Question
By v8dve in forum FundamentalsReplies: 1Last Post: 05-04-2003, 03:31 AM