    Frigidair Ice Machine R-12 40 Oz :0



    Hey I was just looking at a friends Ice machine and after looking at it I've found thats its low on refrigerant (Still enough in there to get cold but not to make Ice)

    So what I'm thinking is to top it up with R-134a as there is enough R-12 to keep the oil flowing, then eventualy totaly over hual it to use r-134a all out then send in the old mix for disposal.

    Does this sound good?



  2. #2
    Join Date
    Feb 2005
    Location
    Jamaica
    Posts
    121
    Rep Power
    20

    Re: Frigidair Ice Machine R-12 40 Oz :0

    NO, why would you want to top up a R12 with 134a? just do a change over

  3. #3
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Frigidair Ice Machine R-12 40 Oz :0

    becuase the guy just wants it patched an running and doesn't want much ells don with it. I all ready told him that this IS the best option to do a total change over, but he wants it don fast sort of deal, Now logic says that to top it off with R-134a will work just fine. Then when he decides whether he will keep the machine or not do the total retrofit.

    IE He is thinking of replacing it and just wants to get a fiew more months out of it till he decides, once he decides He'll invest in doing it all out.

    So the question is will this work and yeild acceptable resualts? and am I missing any more importand underlying issues?

  4. #4
    Join Date
    Apr 2006
    Location
    UK
    Posts
    77
    Rep Power
    19

    Re: Frigidair Ice Machine R-12 40 Oz :0

    R134a is not a retofit replacent for R12 because of the oil in the comp.R49 is a retrofit gas.You have found the unit short of gas.There must be a leak.You must repair the leak before putting any gas in.Unless it is something loose then you will have to reclaim the gas to repair the leak,you might as well vac then recharge(do the job properly).By just topping up to save him money looses you money.Not your problem.He will have to buy new now or you do the proper job now.If you want to do him a favour tell him you will try to locate the leak for free.If you can't find it he will have to scrap it.If you find it you will be more confident to charge him for a proper retofit and he won't have to buy a new one.

  5. #5
    Join Date
    Apr 2006
    Location
    UK
    Posts
    77
    Rep Power
    19

    Re: Frigidair Ice Machine R-12 40 Oz :0

    I have Retro fitted many R12 systems with R49 it works fine.

  6. #6
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Frigidair Ice Machine R-12 40 Oz :0

    I all ready found and fixed the leak, it was a vibration loosend bolt on the filter dryer and the system still has a good amount of refrigerant in it, just not enough to run at full capacity. Where can I get more info on R-49?

    And since there is so much origional refrigerant oil flow wont be a problem. Pluse I'm confused as I've all ways been told that R-134a was to be used to replace R-12
    Last edited by The MG Pony; 20-05-2006 at 12:04 AM.

  7. #7
    Join Date
    Apr 2006
    Location
    UK
    Posts
    77
    Rep Power
    19

    Re: Frigidair Ice Machine R-12 40 Oz :0

    R 134a is a replacement for R12 in long term in a new system as it has the correct oil (synthetic ester oil)when suplied,but the oil(mineral) in the old R12 system is not compatable with R134a.Waxing of the oil is reported and the oil will not mix with the R134a probably not a problem on a small system. R49 is compatible with both oils synthetic and mineral so you don't have to change the oil.

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Frigidair Ice Machine R-12 40 Oz :0

    Quote Originally Posted by Andy T
    I have Retro fitted many R12 systems with R49 it works fine.
    R49 will be a drop-in for R12 but is something completly different then R134a.

    Go ahead with topping of with R134a, you will wish you never had doen it.
    First, it's a capillary system, it will block.
    Second, what about the mineral oil in the system which you will mix with a refrigerant for synthetic.

    You need to refill it with a drop-in, (we use r401a)
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Frigidair Ice Machine R-12 40 Oz :0

    Ok thank you after doing some more research after you guys mentioned R-49 I found info about R-134a causing the oil to "Crystallize" Its a TXV But still if it will be bad for the machine I would be failing my purpose in a gross degree.

    Quote Originally Posted by Andy T
    oil will not mix with the R134a probably not a problem on a small system. R49
    Thats why I mentioned it having the R-12 as it would be a binary mix and the R-12 would carry the oil, who ever this is useless if the R-134a Will alter the oil its self.

    This is why I asked you, I did look into it and I didn't see all the issues and rather then going ahead I thought I had better ask and now that you guys explained it I decided it was a bad Idea, Thank you.

    Where can I get more info on R-49?

  10. #10
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Frigidair Ice Machine R-12 40 Oz :0

    What about the care 12 products? they are a Propane IsoButane mix aren't they?

Similar Threads

  1. Manitowoc Ice machine taking too long to harvest..
    By nyTroX in forum Trouble Shooting
    Replies: 26
    Last Post: 08-05-2011, 09:39 PM
  2. Machine for producing air heat exchanger
    By Renato RR in forum Tools and Calculators
    Replies: 3
    Last Post: 24-05-2006, 11:20 AM
  3. Elderly Ice cream machine.
    By Onthecut in forum Trouble Shooting
    Replies: 12
    Last Post: 20-11-2005, 11:31 AM
  4. Cattabriga Ice Cream Machine
    By Abe in forum Trouble Shooting
    Replies: 9
    Last Post: 26-04-2003, 01:06 PM
  5. Soft Serve machine won't shut off
    By terrygoodrich in forum Commercial
    Replies: 5
    Last Post: 14-10-2001, 01:02 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •