    Very High Energy Consumption



    Hello

    I have a 2m wide display-fridge which is having a very high energy consumption, I mean, HUGE , something like a welding kit or so,..,

    I was wondering what the causes of this migth be and where I should concentrate my efforts.

    Any help is welcome

    Thank you



  2. #2
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Very High Energy Consumption

    If the condensing unit is located beneath the cabinet, then extend the pipes and locate compressor outside the shop,

    Also fit see through blinds

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Very High Energy Consumption

    What is a huge consumption for you?
    How have you measured this coming to this conclusion?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Very High Energy Consumption

    I think Peter is on the right track. Is the energy use higher than the nameplate rating, or, higher than the owner would like to see?

  5. #5
    gdiaz's Avatar
    gdiaz Guest

    Re: Very High Energy Consumption

    Well, it seems that this fridge is using more than 50% of the electricity in the while shop, and there are many other appliances in the premises, including 2 other coolers 2 and milkshake machines, but when this display fridge is disconnected, the meter goes at less than half the speed. Making a rough estimate, it is costing around £200 a WEEK to run a single fridge!!...

  6. #6
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Very High Energy Consumption

    Where abouts are you diaz? in the UK?

  7. #7
    gdiaz's Avatar
    gdiaz Guest

    Re: Very High Energy Consumption

    Yes Abe, in the UK Cheltenham. Cheers

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Very High Energy Consumption

    An open (is it open?) refrigerated display is something which consumes always a lot of energy.
    You can try to install night-shades for it, increase temperature during the night 2K to 4 K, ...
    A counter needs +/- 400 to 500 W/meter, an open display +/- 1000 W/meter, even 1500 W/m
    Last edited by Peter_1; 17-01-2007 at 04:53 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Very High Energy Consumption

    i doubt its £200 a week! think it blow the fuse constantly,been there lots of times with this, blow the condenser nice and clean,check the running current is o/k agaist the plate,gas charge o/k and cuts in/out on the t/stat,and if all thats as it should be,thats as good as it gets,if not sort the problem,thing is the recent explosion in energy prices is hurting everyone big time and machines with large units and open tops etc are very thirsty,as said up the posts you could put the unit out side that allways helps but it needs to be a DX system[expansion valve]. cheers.

  10. #10
    Join Date
    Apr 2005
    Location
    Sheffield, England
    Age
    62
    Posts
    43
    Rep Power
    0

    Re: Very High Energy Consumption

    What type of defrost system has it, is it an electrical heater tape, or has it a heated drain sump. I wounld check to see if these are on all the time.

  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Very High Energy Consumption

    Have you checked the amp draw? from this it is quite easy the determine the cost of running the unit

  12. #12
    rbartlett's Avatar
    rbartlett Guest

    Re: Very High Energy Consumption

    Quote Originally Posted by gdiaz
    Yes Abe, in the UK Cheltenham. Cheers
    have you called a fridge company as i can recommend a few there?

    cheers

    richard

  13. #13
    Join Date
    Jan 2007
    Location
    USA
    Posts
    37
    Rep Power
    0

    Re: Very High Energy Consumption

    Check To See If The Compressor Is Running All The Time And Make Sure Your Defrost Timer Is Not Defrosting Wile It Is Running

Similar Threads

  1. Helpful information
    By chemi-cool in forum Tools and Calculators
    Replies: 2
    Last Post: 30-10-2010, 07:00 PM
  2. Energy Conservation
    By US Iceman in forum Technical Speculations
    Replies: 20
    Last Post: 20-07-2010, 10:52 AM
  3. need energy consumption data
    By gokhan in forum Technical Discussions
    Replies: 2
    Last Post: 25-05-2006, 12:48 AM
  4. A question about energy efficiency rating in Europe
    By pcdata76 in forum Fundamentals
    Replies: 1
    Last Post: 22-05-2006, 10:17 AM
  5. Direct Energy Consumption Question
    By v8dve in forum Fundamentals
    Replies: 1
    Last Post: 05-04-2003, 03:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •