    Question Moisture loss calculation



    Hi Guys,
    Can one of you clever guys tell me how to work out how much moisture is lost when air travels over a coil. If for example air on is 32°C and 85% RH, and the coil temperature is +5°C, what would the RH be of the air leaving the coil if it was, say 12°C?
    Can someone explain how to read this from a psychrometric chart please?

    Thanks



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Moisture loss calculation

    It is impossible to determine from your data.
    I can tell you which RH is the air leaving the coil, from the air temperature leaving the coil. But not just on the coil temperature, because the efficiency of heat transfer depends on the type and geometry of the coil.

  3. #3
    Join Date
    Jun 2003
    Location
    Scotland
    Age
    52
    Posts
    13
    Rep Power
    0

    Re: Moisture loss calculation

    Thanks for your response NoNickName. So what would the RH be on air leaving at 12°C then, and what other data would you need to know?

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Moisture loss calculation

    32°C 85% have an absolute water content of 25.8 g/Kg and dewpoint of 29.2°C
    Any temperature lower than the dewpoint is saturated, that is 12°C is 100% humidity.
    The water content at 12°C 100% is 8.7 g/Kg.
    The difference is 17.1 g/Kg of dehumidification.
    1 Kg of air is 1m3 approx.
    That is your moisture removal would 17grams of water for each cubic meter crossing the coil.
    For 1000m3/h of air flow, that would sum up in 17Kg of condensate per hour.

  5. #5
    Join Date
    Jun 2003
    Location
    Scotland
    Age
    52
    Posts
    13
    Rep Power
    0

    Re: Moisture loss calculation

    Thanks again NoNickName, that helps. So would I be correct in saying then, if I wanted 12°C off at 50% RH, then I would need to have 2°C off, and re-heat it to 12°C, or am I way off the mark?
    Sorry if I am sounding real thick, but I am just trying to learn a bit how it works.

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Moisture loss calculation

    Yes, you are right, but I don't see any commercially feasible way to have 12°C 50% starting from 32°C 85%. Unless it is all recirculated air, and in this case the off and on coil condition will continuously change until setpoint.

  7. #7
    Join Date
    Jun 2003
    Location
    Scotland
    Age
    52
    Posts
    13
    Rep Power
    0

    Re: Moisture loss calculation

    Hi NoNickName,
    What I have here is fresh air on at 32°C 85% RH, the coil has a glycol mixture entering at 5°C and leaving at 8°C. The air off is 12°C 70% RH. It then travels through ducting to supply some cabins. When it reaches the cabins the temperature has increased to around 22 - 23 °C 38% RH.
    I would like to have about 23°C 50% RH in the cabins. With the coil as it is, would the only way of increasing the humidity be to have a water mist injection in the air after the coil?

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Moisture loss calculation

    Quote Originally Posted by gregorm
    Hi NoNickName,
    What I have here is fresh air on at 32°C 85% RH, the coil has a glycol mixture entering at 5°C and leaving at 8°C. The air off is 12°C 70% RH.
    This is impossible. Can't be 70%, it must be 99%.
    Or it is not 32°C 85%

  9. #9
    Join Date
    Jun 2003
    Location
    Scotland
    Age
    52
    Posts
    13
    Rep Power
    0

    Re: Moisture loss calculation

    Apologies, it is drawn through the coil by a belt driven centrifugal fan, and therefore picks up heat off the motor. The point I was able to measure it was at the fan outlet, here it was 12°C 70% RH. Does this make more sense?

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Moisture loss calculation

    Quote Originally Posted by gregorm
    Apologies, it is drawn through the coil by a belt driven centrifugal fan, and therefore picks up heat off the motor. The point I was able to measure it was at the fan outlet, here it was 12°C 70% RH. Does this make more sense?
    Well, it depends how much is the fan gain to the air flow.
    Why are you using total fresh air? Is it a requirement?

    For your question, there are many possibilities of increasing humidity, from ultrasonic humidifiers, to electrodes steam humidifiers, to microsprayers...

  11. #11
    Join Date
    Jun 2003
    Location
    Scotland
    Age
    52
    Posts
    13
    Rep Power
    0

    Re: Moisture loss calculation

    I don't know why it was designed like that, the other ones have a return and mix the fresh air with the recirculated air.
    Thanks for bearing with me, I think I have a better understanding now of the temperature & humidity relationships.

  12. #12
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Moisture loss calculation

    Glad I helped somehow.

  13. #13
    rbartlett's Avatar
    rbartlett Guest

    Re: Moisture loss calculation

    Quote Originally Posted by NoNickName
    This is impossible. Can't be 70%, it must be 99%.
    Or it is not 32°C 85%
    I'm not too sure but is this related to this confusion?

    http://www.hvacrforums.com/showthread.php?p=91#post91


    cheers

    richard

  14. #14
    Join Date
    Jun 2003
    Location
    Scotland
    Age
    52
    Posts
    13
    Rep Power
    0

    Re: Moisture loss calculation

    That looks an interesting one, do you know the answer Richard?

    Greg

  15. #15
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Moisture loss calculation

    Quote Originally Posted by rbartlett
    I'm not too sure but is this related to this confusion?
    Quite an interesting method to hide advertising.

  16. #16
    Join Date
    May 2006
    Location
    Xi an, China
    Age
    51
    Posts
    65
    Rep Power
    19

    Re: Moisture loss calculation

    Except the words I don't understand, it looks like frosting

Similar Threads

  1. Heat Load calculation for residential jobs
    By Herschmidt in forum Air Conditioning
    Replies: 2
    Last Post: 12-05-2008, 11:50 PM
  2. Moisture
    By Abe in forum Trouble Shooting
    Replies: 29
    Last Post: 07-08-2007, 05:50 PM
  3. Moisture in Propane Liquid
    By Nizar in forum Refrigerants
    Replies: 4
    Last Post: 24-07-2006, 04:12 PM
  4. calculation errors
    By Servicefrigo in forum Tools and Calculators
    Replies: 4
    Last Post: 11-02-2005, 01:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •