H11 relates to the inverter compressor operation or inverter PCB.
First check comp windings :- are the readings balanced between terminals and open circuit to earth? Yes & No respectively hopefully.
Then check compressor start current - these are soft start (approx 0.5to 1.0 Amp). If drawing 10+ Amps then PCB OK but seized compressor.
Rgds
Loops