Thread: Expansion valve
06-05-2006, 08:10 AM #1
Expansion valve
Does someone know which brand this valve is?
I thought a Flica or an Egelhof.
On the valve is stamped AO - TA6 - and R12
Picture is mobile phone qualityLast edited by Peter_1; 06-05-2006 at 01:41 PM.
06-05-2006, 08:14 AM #2
Re: Expansion valve
Additional questions.
1: does someone know the capacity of this valve at -10°C(14°F) and 35°C (95°F) condensing on R12?
2: Does someone know of a valve straight in/straight out (1/2 in and 5/8 out)It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
06-05-2006, 08:20 AM #3
Re: Expansion valve
Capacity must be something around 13 kW (44357 BTU/hr/3.696 TR) because it's connected to a Bitzer 4TC-8.2Y
07-05-2006, 05:06 PM #4
Re: Expansion valve
sporlan do one, will have to cut the flares off and braze it in,choice of power heads,cant realy help with numbers,sorry,just watch the super heat is not wide open and floods the compressor on start up,as you can tell it caught me out.
Fitting an expansion valve question
By Larry2 in forum Air ConditioningReplies: 20Last Post: 08-04-2008, 04:17 PM -
expansion valve aint cold
By justinworne in forum Trouble ShootingReplies: 6Last Post: 26-07-2006, 10:52 PM -
I want to find detailed files about ALCO zz thermo expansion valve
By brightfu1 in forum FundamentalsReplies: 2Last Post: 07-09-2005, 03:07 PM -
pressure drop between expansion valve and distributor
By aygul in forum Technical SpeculationsReplies: 10Last Post: 22-01-2004, 09:47 AM -
Oversizing EXV electronic expansion valve
By aygul in forum Technical DiscussionsReplies: 5Last Post: 20-11-2003, 01:00 PM