    Need help to get more info on Copeland hermetic



    Copeland RSN2-0050-IAA Compessor
    115v /1PH /60Hz
    Medium tempitur R-12 compressor
    4,240 BTU/h at 20F; -6.67C; 266.49K
    FLA-9.0A ( 1035W ); LRA-51.0A
    850 watts < ?
    600Ml Minerol Oil

    This is what I sort of know about it, what I need to get is a simple straight for sure answer on it's tonnage!

    1/3 Ton Sounds close (It's a bit higher according to my math)

    Second I need to know what do I need for a hard start kit for it as I'll be using it in a pump down system.

    Third: Will R-290 be too hard on this unit? or an R-290/R-134a Mix be better?



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Need help to get more info on Copeland hermetic

    And all so, I rather abused the poor thing when I was first learning, so needles to say it needs a very good wash inside, what Can I use thats not specialized as I don't have access or the money for any specialized flushes.

    Would Varithol work? Acetone mix? (I know acetone won't work as it would eat the varnish of the motor windings, but I'm using it as an example)

    Any and all help will be greatly apreciated thanks!

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Need help to get more info on Copeland hermetic

    Whats's BTU?
    Provide the proper SI between brackets please, much easier to read, at least for me.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Need help to get more info on Copeland hermetic

    SI ?

    (4,240 BTU/h at 20F)

    plant specs:

    Copeland RSN2-0050-IAA Compessor

    115v /1PH /60Hz

    Medium tempitur R-12 compressor

    4,240 BTU/h at 20F; -6.67C; 266.49K

    FLA-9.0A ( 1035W ); LRA-51.0A

    600Ml Minerol Oil

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Need help to get more info on Copeland hermetic

    BTU in SI is kW,
    °F in SI is °C,
    psi in SI is Pa
    We're use to work in SI
    ......
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Need help to get more info on Copeland hermetic

    Ah Metric, I've never heard the term si befor. I'm bit of an oddity here in Canada we use metric but being stuck next to the americans we are forced to use imperial as well for some things it is easier to use imperial, and I rather enjoy the TON method of ratings it keeps the numbers small and simple.

    I have no idea as to the Metric ratings as there are non, that is the raw data of the compressor and thats what I don't know hence why I'm asking if any one can get the data as thus far I haven't been able too!

    If I knew the data for certainty I wouldn't be asking LOL

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Need help to get more info on Copeland hermetic

    Download once Uconeer, the free conversion software.

    Well, these raw data can be converted to other units.

    Well, for me .. if we talk about tons...a ton is 1000kg, so 1/3 ton is 300 kg...a little bit heavy for such a small compressor
    You see, not that difficult at all.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Need help to get more info on Copeland hermetic

    cute. but thats the thing I have no certain data on the compressor! thats what I'm trying to find out

    What is its definate ratings either imperial or metric.

    Will it handle: R-290, R-22, and so on

    thats what I'm trying to do!

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Need help to get more info on Copeland hermetic

    1TR (1 ton refrigeration) is 12000 btu I believe.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Need help to get more info on Copeland hermetic

    ya thats right.

    For converting BTUs to Tonns:

    (1 / 12,000) * Zbtu/h = T%

    Where Z = Your BTU rating
    T% = Tonnage in a percent

    ^Theres a simple formula I wrote for converting (I'm sure others have made a far better ones then mine but it works)

  11. #11
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Need help to get more info on Copeland hermetic

    Here is a program printout from the Copeland software. I'm not sure if the 4 in the model number is for a newer model, but the rest of the information seems similar.

    As to try to answer your other question...

    Will it handle: R-290, R-22, and so on?
    I don't think so. R-22 and R-290 will have higher mass flow rates for any operating condition other than R-12. My guess is you will overload the motor.

    I've never heard the term SI before
    If I remember this properly it stands for System International, if I translated the French correctly.

    I used to do a fair amount of work for Pacific Rim clients and they used metric, which can be a bit different that SI, so you have to watch the units very closely.

    Peter & Brian, I could not get the program to convert the data into SI. Sorry...
    Attached Files Attached Files

  12. #12
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Need help to get more info on Copeland hermetic

    Quote Originally Posted by Peter_1
    BTU in SI is kW,
    °F in SI is °C,
    psi in SI is Pa
    We're use to work in SI
    ......
    Peter try this:

    http://www.gordonengland.co.uk/conversion/sibase.htm
    Last edited by wambat; 06-05-2006 at 03:07 AM.

  13. #13
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Need help to get more info on Copeland hermetic

    Ok so what I figured I have to use R-134a /R-600a mix

    I don't quite understand the table, exactly how meny tons is the compressor rated for?

    All I know is it consums 9Amps and is rufly 1/2Horse motor, and even then I'm not sure of! Basicly what I'm hoping it will at least handle being cupled to a 1/2Ton TXV?

  14. #14
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Need help to get more info on Copeland hermetic

    I don't quite understand the table, exactly how many tons is the compressor rated for?
    Look at the evaporating temperature and condensing temperature you want to operate at. The capacity (C in the table) is given in Btu/hour. Divide the Btu/hour by 12,000 Btu/hour-Ton. This gives you the Tons (or TR for Tons of Refrigeration).

    Example: 4,000 Btu/hour / 12,000 = 0.33 TR

    This rating is also dependent on the rating conditions specified on the sheet. If the operating conditions are different than those specified, the capacity can be more or less depending on what variable changes.

    The capacity and all of the other data will change if the refrigerant type is changed. A 1/3 TR compressor on R-12 can be different than a 1/3 TR compressor for R-22.

    I'm not sure why you are building a system??

    The TXV should be matched for the same operating conditions as the compressor. A 1/2 TR TXV used on a 1/3 TR compressor will not work right.

  15. #15
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Need help to get more info on Copeland hermetic

    Ok thanks.

    Why is to simply design and build a system using proper design principles and properly engineer it within X degrees. the perpos, right now just to get cold, it has no finite perpos.

    but whats with the :

    C (Capasity?)
    P ( ? )
    A ( ? )
    M (Mass flow)
    E (Energy)

    Thing?
    Last edited by The MG Pony; 06-05-2006 at 05:39 AM.

  16. #16
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Need help to get more info on Copeland hermetic

    So at 32C with an evap @ -3.1C it can do 6100BTU/h ie 1/2 Ton

    What size Capacitor do I need for Hard starts and do I need to replace the current relay? The old system used a rather larg cap tube so I doubt it has a hard start all ready there.
    Last edited by The MG Pony; 06-05-2006 at 07:31 AM.

  17. #17
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Need help to get more info on Copeland hermetic

    I think the P = power = watts; A = amps

    I don't know what the % is for.

  18. #18
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Need help to get more info on Copeland hermetic

    Quote Originally Posted by wambat
    Wambat, thanks.
    It's not that I don't understand these units but if I have to translate this for every post, then I'm more busy with converting the units then answering the post itselves.

    I personally find that this is the responsibility of the poster if he wants to be helped by as many as possible posters.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  19. #19
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Need help to get more info on Copeland hermetic

    well again I'm trying to identify WHAT the info is, so you cant translate zerro! if I had the info I could project the rest fairly well. but identing the compressors details is the hard part. But thanks to US Iceman I now have some idea of the compressors specs and rates, thats what I was trying to find to make sure it was within its ratings with the TXV and thank fully it is!

    The compressor will do 6100BTU/h (1/2 ton) @ a condensing temp of 32.2C & and evap @ -3.9C

    HS 90 to 123psig Max ; LS 20 to 35psig Max depending on which refrigerant used (R-12; R-134a: R-401a, 401B)

    But in Mid summer here in BC it gets up to a max of 40C in the city with an average mean of 35C So Now I can plot out over all performance through out summer and at what Capacity I can reasonably expect it to opperate. More info though the better

  20. #20
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Need help to get more info on Copeland hermetic

    Here's the pictures of the progress so far
    Last edited by The MG Pony; 09-11-2007 at 07:01 PM.

  21. #21
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Need help to get more info on Copeland hermetic

    This seems indeed an old unit.
    I did't know that HP was making condensors in the past
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  22. #22
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Need help to get more info on Copeland hermetic

    ya, 1973. I added the lowpressur switch and the reciver, cleaned it up a bit. I personaly like how sturdy the compressor is, wish I could afford to buy one just like it brand new for R-22 so I could us R-290, it is a beautyfull refrigerant

  23. #23
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Need help to get more info on Copeland hermetic

    You should also place a fan shroud around the fan side of the condenser. This will help the condenser to have adequate air flow through it. A fan sticking out in the open will help, but it is not the same as having the fan shroud in place.

  24. #24
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Need help to get more info on Copeland hermetic

    It will be further shrouded, but right now I am building it

Similar Threads

  1. samsung info
    By cruzeiros in forum Air Conditioning
    Replies: 0
    Last Post: 13-01-2006, 12:16 PM
  2. Angelopo Sm2l Error E2 Please Info About This Error
    By CHARLIEZOLO in forum Commercial
    Replies: 0
    Last Post: 22-12-2005, 03:47 AM
  3. fujitsu tech info
    By Krups in forum Air Conditioning
    Replies: 11
    Last Post: 01-12-2005, 07:41 PM
  4. Usefull General Info
    By Peter_1 in forum Fundamentals
    Replies: 7
    Last Post: 27-04-2005, 06:13 PM
  5. Looking for chiller info on the web....
    By crazedhick3 in forum Fundamentals
    Replies: 0
    Last Post: 11-04-2003, 04:41 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •