Results 1 to 3 of 3
Thread: Daikin Super Inverter
-
21-02-2016, 06:17 PM #1
Daikin Super Inverter
I just install a new pc board to this condensing unit and it just wont work error code is UA can someone assist
-
21-02-2016, 06:34 PM #2
Re: Daikin Super Inverter
https://www.climatecenter.co.uk/wcss...in-trouble.pdf
Looks like there are some dip switches or similar that need setting for it to work, its wired wrong, or its the wrong board.Mostly found in Oxfordshire, UK :)
-
21-02-2016, 08:43 PM #3
Re: Daikin Super Inverter
why was the board changed?- what was the original fault?
some daikin pcbs req a capacity setplug that tells the pcb the size of the outdoor unit