    Vibration in refrigerant piping



    Here is another topic that will surely put you to sleep. Or, maybe it will keep you awake during the night.

    I have long been fascinated by the impact of vibration and noise in refrigerant piping. As you will see in the files below the manufacturers are aware of this and are offering some general guidance on this particular subject.

    In general terms, the problem is associated with the acoustic velocity (speed of sound) of the refrigerant for the specific operating condition. The other important aspect is the frequency of the gas pulsations from the compressor.

    Screw compressors should be treated differently than reciprocating compressors since the gas pulsations are different for both types and are also dependent on rotating speed.

    By determining the above you can then calculate the "piping lengths" to minimize the impact of vibration and the resulting noise.

    The information below is not a set of documents that provides all of the information, but they are sufficient to show an interesting concept to consider.

    http://www.carlylecompressor.com/Fil...f?SMSESSION=NO
    (740 kb)

    http://www.bitzer.de/_doc/s/st-630-1.pdf
    (323 kb)



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Vibration in refrigerant piping

    Recently we have adopted a new refrigerant piping, at least on the discharge. It is a flexible pipe, imported in Italy by WIGAM, and helps reducing pulsation and noise very much.

    http://www.wigam.com/web/prodotti.as...odice=infinity

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Vibration in refrigerant piping

    The corrugated tubing used is probably providing sufficient resistance to disturb the pulsations to reduce the vibrations and noise. This would have a similar effect as using an orifice plate to restrict the pulsations.

    This tubing looks very similar to what I remember from the past. Copeland used to have a flexible tubing that was used for the Sentronic oil safety switch. This was much better than the old style capillary tubes with flare nuts.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Vibration in refrigerant piping

    We order these at a company +/- 1 km from our company
    http://www.sisahp.be/products/specifiek.php

    Used those some times, but they're sometimes not flexible enough to bend them some times/day in small diameters like in a sliding counter.
    We get the couplings and the hose separately, we install them without crimping and thereafter, we go back to crimp them.
    We also use the system of Burgaflex (The Netherlands) http://www.burgaflex.com/burgaflex.html a litlle bit more expensive but more flexible.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Vibration in refrigerant piping

    Personally, I find mufflers not that usefull but an oil separator solved already twice a pulsation problem heard especially in the condensor coil where we selected a low noise.
    But all the noise was coming form the pulsations in the discharge line (discharge in 1 case selected at 7 m/s to avoid pulsations)
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Vibration in refrigerant piping

    Sometimes it is not just the speed of the refrigerant moving in the tubing. The speed of sound in the refrigerant depends on the quality (liquid or vapor).

    The frequency of the gas pulsations and the speed of sound in the refrigerant can also cause vibrations.

    Vibration can be generated by mechanical forces or by acoustics also. The oil separator probably reduced the vibration because of the larger volume of the oil separator relative to the discharge line.

Similar Threads

  1. R600 Refrigerant.
    By tonydeith in forum Refrigerants
    Replies: 14
    Last Post: 21-04-2011, 08:52 AM
  2. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  3. Replies: 2
    Last Post: 16-11-2005, 05:34 PM
  4. Liquid refrigerant and bubles in sightglass
    By aygul in forum Trouble Shooting
    Replies: 2
    Last Post: 30-08-2003, 09:07 PM
  5. Refrigerant Reclamation
    By herefishy in forum Commercial
    Replies: 6
    Last Post: 23-07-2003, 08:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •