Thread: Pump Pressure

  1. #1
    Join Date
    Dec 2005
    Location
    u.k.
    Posts
    17
    Rep Power
    0

    Talking Pump Pressure



    Got a bit of a problem, I am commissioning a pump circ Ammonia system running at -40c, I am struggling to get any sensible pump pressure. We are using Witt pumps, if I dead end the system I get pressure but as soon as I open it up again everyting goes imediately to suction pressure, I have tried increasing surge drum pressure and level neither of which seem to have had any effect, there is also no oil in the pumps (checked that first!) anyone got any ideas????



  2. #2
    Craig Nicholson's Avatar
    Craig Nicholson Guest

    Re: Pump Pressure

    Clivet .

    What type of Witt pumps are you using -GP51 ,52 etc.
    What is your NPSH and what does your piping layout
    to your pump look like .

    Please send info and i will assist you with your problem.

    Regards
    Craig Nicholson

  3. #3
    Join Date
    Dec 2005
    Location
    u.k.
    Posts
    17
    Rep Power
    0

    Re: Pump Pressure

    Craig
    In short I dont know without checking what my pump model numbers are and what my NPSH is I wont be back on site until the morning. The piping to the pumps is via a common drop leg from the drum into separate supply legs, the discharge from the pumps goes via check valves into a common liquid line, there is a balance line from the liquid line to the top of the drum and that is currently shut.
    Iv been reading another thread on this site that relates to problems arising from the pump sucyion leg being too close to the wet return line and suffering from pump cavitation as a result.
    I will check things out in the morning and get back to you.

    Clive

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Pump Pressure

    Clivet,

    It sounds like the pump is going into cavitation when the discharge valve is opened.

    Some questions for you:

    1) how much pressure does the pump develop when the discharge valve is closed (dead headed)?

    2) Are you running multiple pumps at the same time on the same vessel?

    3) An easy one: Is the pump rotation correct?

  5. #5
    Join Date
    Apr 2005
    Location
    Adelaide
    Age
    54
    Posts
    10
    Rep Power
    0

    Re: Pump Pressure

    Have you checked to see that your hand regs on the evaps are not to far open?
    If you close all the hand regs down what is the pump pressure?
    Hane you got a minium flow line installed?

  6. #6
    Join Date
    Dec 2005
    Location
    u.k.
    Posts
    17
    Rep Power
    0

    Talking Re: Pump Pressure

    I am running multiple pumps off the same vessel, and indeed of the same leg, when the pumos are deadheaded I get about 4 bar pressure just prior to the regulating valves at the evaps these valves are almost closed at present. As far as the DOR is concerned both pumps show an increase in discharge pressure before the pump check valve when run.
    I think it is quite possible that the pumps are cavitating, I will try runnin with one turned off this morning and see what happens, hanks for your sugestions so far.

    Clive

  7. #7
    Join Date
    Jan 2005
    Location
    Norfolk, U.K
    Age
    44
    Posts
    65
    Rep Power
    20

    Re: Pump Pressure

    there is a balance line from the liquid line to the top of the drum and that is currently shut.
    These should be opened, we normally have ours open about 3 or 3 1/2 turns.

    3) An easy one: Is the pump rotation correct?
    an easy one but check to be sure, also are the pumps brand new?, i have come across a gp 51 before which someone had overhauled and the impeler had been installed the wrong way round,

    Have you checked to see that your hand regs on the evaps are not to far open?
    If you close all the hand regs down what is the pump pressure?
    Have come across this in the past, it's well worth playing about with the settings on these valves.

    Have you checked the inlet filters in the pumps? on one of my systems there are no oil separators, oil is returned via oil rectification, these means there is a lot of oil floating around the hole system and did give us problems with cavitation, during comisioning we were constantly changing these, and in the end we used a stanly knife to remove the fine gauze from the filter this made a massive difference but i wouldnt do this until your sure the system is clean.

    Also check liquid line strainers.

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Pump Pressure

    I get about 4 bar pressure just prior to the regulating valves at the evaps these valves are almost closed at present
    OK. How much pressure is the pump supposed to generate?

    The pressure at the regulating valves (which I assume are hand expansion valves) is the sum of the pump head (pressure that the pump can generate) plus the surge drum vapor pressure minus all of the pressure losses due to friction and elevation.

    If you are getting 4 bar of pressure at the -40C evaporators the pumps are indeed pumping.

    If the pump discharge pressure goes to the surge drum pressure when the pump discharge valve is opened, it sounds like the hand expansion valves are wide open.

    The pump is trying to produce a lot of flow with very little head developed. This can substantially increase the NPSH required by the pump and cause cavitation.

    Are multiple pumps required with simultaneous operation, or will one pump provide sufficient liquid flow?

  9. #9
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,042
    Blog Entries
    4
    Rep Power
    31

    Re: Pump Pressure

    When you close the discharge valves, does it take a few seconds for the pressure to reach 4 bar?

    Can you get a stable pump pressure if you defrost and shut of some of the consumers?


    does the pump pressure oscilate?


    all of the above indicate that you have to low liquid head on the suction side of the pump.


    Unless you have a bypass valve open, or the pump is running the wrong way, I'd say it's indication of a to small ammonia charge.
    -Cheers-

    Tycho

  10. #10
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: Pump Pressure

    Hello Clivet,

    here are some notes from Witt GP operation&installation manual:

    To be sure the pump will operate even at a low-pressure difference resulting in maximum capacity, the diameter of the downleg to the pump should be executed as mentioned in the table below

    Required diameter of the downleg to the pump

    GP 41 DN80(3”)
    GP 42 DN80(3“)
    GP 51a DN100(4“)
    GP 51 DN 100(4“)
    GP 52 DN150(6“)

    Discharge pipe is not so critical but liquid velocity up tp 1,5 m/s is normally recomended.

    A by-pass valve (adjustable) is required if the system design or the evaporator installation allow closed discharge running. Operating refrigerant pumps partially at or at a fully closed throttled condition is not allowed and will damage the refrigerant pump! The adjustable by-pass valve shall be sized DN 20.

    The pump shall be connected using a vertical pipeline to the separator. To prevent interaction between pumps it is advised that each pump be connected individually to the separator.

    Only when a stand-by pump is installed may two pumps be connected to a common downleg.

    Capacity can be too low due to:

    - direction of rotation wrong
    - frequency of the pump too low
    - stop valves behind the pumps closed
    - too much gas in liquid
    - liquid level in separator too low
    - valves on cooler closed
    - regulating valve not opened far enough
    - contamination is blocking the piping system
    - non return valve of an other pump leakes
    - power supply not right, working on only 2 phases
    - impellers worn out
    - oil in pump at low temperature
    - not sufficient suction head

    - Intermediate pieces do not align hope your pumps are new and this is not a cause.


    Try to run only one pump with discharge valve open 2-3 turns, when you obtain some stable pressure try to open discharge valve more until pressure start to drop. At that point stop and close discharge valve for 1/4 of turn and leave it.

    You can repeat this with another pump and see if everything is the same (pressure, consumption..) maybe to switch on both pumps simuntaneously and check what happen with pressure....if pressure remain ok, if not, try to run only one pump and then you can start to play with RV on evaporator/s

    Best regards,

    Josip

  11. #11
    Join Date
    Dec 2005
    Location
    u.k.
    Posts
    17
    Rep Power
    0

    Re: Pump Pressure

    Gentlemen
    Thank you for your ideas and help, using your thoughts and think logically I decided that the cavitation route was the best option to follow, thus I turned off one of the pumps from"the common drop leg" and lo, pump pressure was forthcoming.
    Thanks chaps
    Clive

  12. #12
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Pump Pressure

    Clivet, where can we send the invoice?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. liquid ammonia pump calvitation
    By Kathleen in forum Trouble Shooting
    Replies: 23
    Last Post: 20-05-2011, 02:18 AM
  2. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  3. pressure drop of pump return line ammonia
    By Moeller in forum Fundamentals
    Replies: 5
    Last Post: 04-09-2007, 05:21 AM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •