    Temperature Sensor



    Hi,

    I have a Daikin Model # FDYP100 Inverter Air Conditioning. At present the control panel and therefore the temperature senor that controls the System is in the Lounge Room. How do I change it so the system uses the sensor in the inlet ducting? I have an open fire in the lounge and with it on the A/C sense the Temperature is too high so it switches off. The problem is that then the rest of the house is to cold. Thanks for any help you can offer.


    Regards

    Ian



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Temperature Sensor

    The sensor in the controller is not used normally. The control is via a return air sensor within the indoor unit. A small bead thermistor can be seen when you take out the filters.

    You can check by using the buttons on the remote though. Open the flap and press and hold the bottom "Test " button until the display reads 10.
    Now, press the "timer up" button until the first code number reads 2.
    Now press the "timer down" button until the second code reads 02.
    Now press the button directly above the "test" button and let go. Now press the test button and you will see "88" displayed for a few seconds. When the controller goes back to a normal display it will then control from the return air sensor.

    Job done
    Last edited by frank; 19-04-2006 at 08:21 AM.

  3. #3
    Teddy's Avatar
    Teddy Guest

    Re: Temperature Sensor

    Thanks Frank, I'll give it a try.

  4. #4
    Teddy's Avatar
    Teddy Guest

    Re: Temperature Sensor

    I tried it out and it did worked so thanks for the help. I can understand what the first number for but what does the 01 and 02 mean? Also is there some where that you can get a list of what the rest of the test codes mean?

  5. #5
    Join Date
    Apr 2006
    Location
    Sydney Australia
    Age
    47
    Posts
    6
    Rep Power
    0

    Re: Temperature Sensor

    02 is when you set it back to factory setting (Return Air)

    01 is part of the process carried out to sense it at the wall controller

    To sense at the wall controller you will need to go to Setting 10 2_01 Press the confirmation/ timer cancellation button

    Hold test till you get setting 40

    Hold test till you get setting 50

    Timer up till 4 Timer down to 01

    Press the confirmation/ timer cancellation button

    Tap test once then control will appear as 88, it's just initialising and will return to normal.

    NOTE - Be careful in the 50 settings if you set the wrong code other than 4_01 the temperature display on the controller disappears and you need to replace the indoor board to rectify the problem.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Temperature Sensor

    Quote Originally Posted by Teddy
    I tried it out and it did worked so thanks for the help. I can understand what the first number for but what does the 01 and 02 mean? Also is there some where that you can get a list of what the rest of the test codes mean?
    have a look here http://www.refrigeration-engineer.co...68&postcount=2

  7. #7
    Teddy's Avatar
    Teddy Guest

    Re: Temperature Sensor

    OK that make sense, but if that the second number is the sensors to use, what is the first number. I have 0 to 3 as the first number. I thought that would have been the sensors to use. I have discovered that I have 3 sensors in my system. One near the back door, one in the lounge and the return air senor so should the second number have 01, 02 and 03. Thanks for all the help so far.

Similar Threads

  1. re ref. circuit
    By shsalameh in forum Fundamentals
    Replies: 5
    Last Post: 06-08-2007, 12:59 PM
  2. Q=? h1=? mechanical schematics
    By fridg in forum Technical Speculations
    Replies: 22
    Last Post: 19-03-2006, 01:43 PM
  3. fujitsu tech info
    By Krups in forum Air Conditioning
    Replies: 11
    Last Post: 01-12-2005, 07:41 PM
  4. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM
  5. Replies: 5
    Last Post: 16-10-2002, 12:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •