    Gas / Liquid ratio in Condenser



    Does anyone know if it is possible to calculate the ratio of gas to liquid in a condenser within an air conditioning system within a military vehicle.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Gas / Liquid ratio in Condenser

    I suppose the easiest way would be to use the Mollier chart.

  3. #3
    Join Date
    Apr 2006
    Location
    Hampshire
    Posts
    5
    Rep Power
    0

    Re: Gas / Liquid ratio in Condenser

    Just had a scan over the internet looking at the mollier chart. Not entirely sure how they work. I am using R134a for my system in an ambient temperature of 35 degree, is it possible to use such a chart for this process.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Gas / Liquid ratio in Condenser

    Yes it is. It may also be known as a p/h chart.
    Last edited by frank; 11-04-2006 at 03:39 PM. Reason: Typo

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Gas / Liquid ratio in Condenser

    Coolpack by NIST will help you.
    It is free to download and will simulate the gas/liquid percentages upon custom coil design.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Gas / Liquid ratio in Condenser

    I know Coolpack from the Danish Technical University.
    Is this another Coolpack package?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Gas / Liquid ratio in Condenser

    Sorry, I stand corrected. I meant EVAP-COND by NIST, the national institute for standards of USA

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Gas / Liquid ratio in Condenser

    You could also determine the liquid level in a DX evaporator using a temp probe. Measure the temps up the coil bends and note the temps. As you approach the outlet the temp will increase significantly indicating the phase change area.

    All you have to do then is calculate the proportion of coil with the lower temps against the proportion with higher temps.

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Gas / Liquid ratio in Condenser

    Franks method is very straightforward and an easy way to check.

    As an estimate for an air cooled condenser (with no head pressure controls, and you will not have these on a vehicle) is to use about 85-90% of the condenser volume for the vapor volume. About 10-15% will be the liquid volume.

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Gas / Liquid ratio in Condenser

    I've got to ask the quesion though? - why do you want to calculate the liquid/vapour ratio?

Similar Threads

  1. Subcooling & Refrigerants
    By US Iceman in forum Fundamentals
    Replies: 40
    Last Post: 29-04-2006, 02:59 AM
  2. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM
  3. hot discharge air from C.U
    By ong in forum Fundamentals
    Replies: 48
    Last Post: 29-07-2005, 06:24 AM
  4. hvac/r terminology
    By Prof Sporlan in forum Fundamentals
    Replies: 18
    Last Post: 06-04-2002, 03:47 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •