Air in the refrigerant circuit - please help
Refrigerant circuit has taken air because the evaporator it has holes. Result is the pressure in the depression to be off limits. What you propose to me making? Thanks
-
16-06-2010, 10:24 PM #2
Re: Air in the refrigerant circuit - please help
Recover the refrigerant using an inline drier filter. Replace evaporator
-
17-06-2010, 03:12 AM #3
Re: Air in the refrigerant circuit - please help
You could then blow off (into another large cylinder) about 10% of the gas, check it with a PT chart and if all good reuse the gas. Most of the non condensable gas will sit on the top.
-
17-06-2010, 05:17 PM #4
Re: Air in the refrigerant circuit - please help
i don't think there mutch left to recover. you can presurise the condensor or evaporator whit NGO, repair the leaks, triple vacuum and refill whit exact amound of refrig. a dirty job, but rewarding if it is nicely done.
Ice
-
17-06-2010, 06:28 PM #5
Re: Air in the refrigerant circuit - please help
If he is able to recover gas ! then this idea is best suited.
-
17-06-2010, 06:38 PM #6
Re: Air in the refrigerant circuit - please help
a smart technician is always able to do a recover. so many ways if you have gauges.
i did mi first whit an old compressor and torch, some 35years ago.
Ice
-
17-06-2010, 07:03 PM #7
Re: Air in the refrigerant circuit - please help
There are many ways of recovery!
only if gas is present!
If gas is leaking , inside gas will not be
contaminated.
rgdS
-
17-06-2010, 11:38 PM #8
Re: Air in the refrigerant circuit - please help
Good chance if it's sucked in a gutful of air, the oil is going to have a stack of moisture in it. Make sure you treat it like a burnout and put a burnout dryer in and try and get rid of the acids and moisture once you have the evaporator sealed up.
Similar Threads
-
Superheat and Subcooling
By Chunk in forum FundamentalsReplies: 42Last Post: 15-01-2011, 01:24 AM -
refrigerant circuit
By pete seyfried in forum TrainingReplies: 1Last Post: 19-04-2010, 06:57 AM -
humidity inside refrigerant circuit
By sakly in forum IndustrialReplies: 6Last Post: 13-04-2010, 12:12 PM -
fun quiz
By Brian23 in forum New to REReplies: 6Last Post: 02-10-2007, 10:18 PM -
How critical are circut lengths when using a distributor?
By kengineering in forum Technical DiscussionsReplies: 17Last Post: 27-02-2006, 07:35 AM