Results 1 to 2 of 2
Thread: Climaveneta CVM3000 problem
-
27-01-2014, 10:23 PM #1
Climaveneta CVM3000 problem
Hi,
I've a problem with a CVM3000C that has four systems but each of the four systems has a fault that will not reset.
Three of the faults are for a comp overtemp the other is for a HP
None of these are real alarms and the input for each of these is not putting a fault signal into the board.
Has anyone come across this or has any suggestions
-
12-02-2014, 09:59 PM #2
Re: Climaveneta CVM3000 problem
Hi,
If you have the 240 volt control circuit made but the fault won't clear it's usually a fault on the main PCB ( cvm )
You are best to speak to Climaveneta uk and they will give you a price for a new one.
Good luck.