10-03-2006, 10:05 AM #1
Daikin Indoor Unit
I recently went to maintain a Daikin Indoor unit, model number: FHYC100FJV1 on the remote the was a fault code flashing. fault code: A7. Unfortunatley i do not have the correct book to find out what this fault code is could somebody please help me. cheers
-
10-03-2006, 10:51 AM #2
Re: Daikin Indoor Unit
Swing flap motor error
cheers
richard
-
10-03-2006, 11:16 AM #3
Re: Daikin Indoor Unit
An A7 fault will not stop the system from operating but will flash as a fault.
You can also get this error if you forget to connect the wires between the grille and cassette.(the little push clip)
-
10-03-2006, 11:27 AM #4
Re: Daikin Indoor Unit
Frank
I once got this fault when the interconnect was wrong on a 10kw wall mount..wierd eh?
cheers
richard
-
10-03-2006, 11:35 AM #5
Re: Daikin Indoor Unit
Very Wierd Richard.
I assume it was only the comms and neutral that was incorrect. Normally if this was the case then you wouldn't even get a display on the controller
-
10-03-2006, 11:39 AM #6
Re: Daikin Indoor Unit
indeed it was and everything worked apart from a7 -which I thought was strange as the flap worked !
I re-wired it and it all worked..??
cheers
richard
-
10-03-2006, 12:33 PM #7
Re: Daikin Indoor Unit
cheers lads
-
10-03-2006, 06:52 PM #8
Re: Daikin Indoor Unit
Ebo, try this link
http://www.refrigeration-engineer.co...ghlight=daikin
I had posted the Daikin fault code matrix there earlier, it's a pdf file.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
11-03-2006, 10:23 AM #9
Re: Daikin Indoor Unit
cheers brian
-
14-03-2006, 08:54 PM #10
Re: Daikin Indoor Unit
just thought i would point out as well, that you should test the louvre's in fan only mode, as they will only operate in a thermostat on condition in cooling/heating. Also on old school units sky air series C and D if the louvre motor failed it would hold off the cooling/heating! only way round about it is to replace the motor.
-
15-03-2006, 03:58 AM #11
Re: Daikin Indoor Unit
Hey since you guys have had Diakin over there much longer then us over here what do you think of it and where does it rate compared Mitsubishi, Sanyo, trane etc etc
McQuay, ABB, Pool Pak, Ebtron, ArticChill, ETI, Governair, Venmar, Ventrol, Grundflos, Diakin, Reznor, Sterling, Trox
Similar Threads
-
Daikin Refnet Position
By puddleboy3 in forum Air ConditioningReplies: 15Last Post: 13-02-2009, 04:12 PM -
Daikin Analyzer
By marc5180 in forum FundamentalsReplies: 10Last Post: 02-08-2008, 07:15 PM -
Daikin Controllers
By airefresco in forum Air ConditioningReplies: 5Last Post: 15-05-2008, 08:08 AM -
Daikin VRV
By nickthefridge in forum Air ConditioningReplies: 10Last Post: 14-10-2007, 01:42 PM -
!!big Daikin Problem!! Codes,u4,pj, And E0
By airconengineer in forum Air ConditioningReplies: 21Last Post: 31-05-2007, 09:04 PM