    Coffin Case Woes



    I am having problems with some coffin cases (Hussman model type - GWIT). That keeps buliding frost in the discharge plenum of the case. The case drains well, and the coil is clear, What are some things I can check?



  2. #2
    Join Date
    Dec 2005
    Location
    South East England
    Age
    56
    Posts
    155
    Rep Power
    19

    Re: Coffin Case Woes

    Increase drip time after defrost
    Noah had to leave the dinosaurs behind as they would've sunk the boat.

  3. #3
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Coffin Case Woes

    Defrost termination tempature set too high.

    No fan delay.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  4. #4
    Join Date
    Mar 2006
    Location
    Canada
    Posts
    13
    Rep Power
    0

    Re: Coffin Case Woes

    Thanks for the replies. The drip times have been increased. The fans run all the time so if I were to install a fan delay I would be preventing the fans from pushing that moist air throughout the case. Is that correct? Also if the defrost termination is set to high how does that affect the build up frost?
    Last edited by Stiff Nipples; 11-03-2006 at 09:01 AM.

  5. #5
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Coffin Case Woes

    Also if the defrost termination is set too high how does that affect the build up frost?
    If it is set too high not only will you defrost the coil but you will turn most of the water into vapour. Which will condense on the back wall, drip down and then refreeze at the bottom.


    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  6. #6
    Join Date
    Dec 2005
    Location
    South East England
    Age
    56
    Posts
    155
    Rep Power
    19

    Re: Coffin Case Woes

    As Chillin Out said you also need a fan delay after the defrost so that any water that is left on the coil is re-frozen instead of being blown out by the fan.
    Noah had to leave the dinosaurs behind as they would've sunk the boat.

  7. #7
    Join Date
    Mar 2006
    Location
    Canada
    Posts
    13
    Rep Power
    0

    Re: Coffin Case Woes

    Thanks again I will take it all into account. Do either of you guys know a good site for literature for theses older style cases. The ones I work on are ussually refurbished
    And a bad refurbish (coat of paint and out the door ). Would like to make sure that the cases come like they should have if they were new.

  8. #8
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Coffin Case Woes

    Instruct the store to use night covers, and provide a single defrost for 60 minutes when the store is closed. I am guessing that you have Gas defrost, but the advice applies to electric as well. One defrost. Make it long enough to circulate warm air throughout the case.

  9. #9
    Join Date
    Mar 2006
    Location
    Canada
    Posts
    13
    Rep Power
    0

    Re: Coffin Case Woes

    The store staff are not reliable enough to ensure that the 288 ft of coffin that eventually encounters the problem will get covered. Also would a defrost of that length be good for the integrity of the product?

  10. #10
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Coffin Case Woes

    One good and complete defrost every 24 hours is your best option regardless of the store's discipline or lack thereof. Clearing the flues and drain pan are an important part of the defrost process, thus a longer defrost only once a day is the best option. Product integrity is best preserved by having as few defrosts as possible. Not by shortening the duration and increasing the frequency, which is an all-too-common occurence.

  11. #11
    Join Date
    Feb 2006
    Location
    Mauritius
    Posts
    22
    Rep Power
    0

    Re: Coffin Case Woes

    We have good results here with two defrosts: One just after store closes and the other about 1 hr before opening, to ensure the coils are clean in the morning.

  12. #12
    Refrig_Controls's Avatar
    Refrig_Controls Guest

    Re: Coffin Case Woes

    One way to accomplish this functionality is to replace the older electromechanical controls with one low cost electronic controller. I work for Carel and we have a solution that would allow you to make adjustments to defrost durations and frequency using one controller. The controller is called a PJ32 and can be found here -

    www.carel.com

  13. #13
    Gary C NM.'s Avatar
    Gary C NM. Guest

    Re: Coffin Case Woes

    We had the same problem in several stores. all with (kool gas) defrost. the best cure I found was to install fan delay switches and increase the drip time. Also found the tech's setting the temps too cold. Warmed back up +5 deg. -10F frozen food & -15F IC.
    and it seems to have fixed most of the problems.
    Note Here in Albuqueerque we have very low humidity, and thin air. May or may not help in a much more humid climate.

  14. #14
    Karl Burke's Avatar
    Karl Burke Guest

    Re: Coffin Case Woes

    Im sorry but I have not been able to identify whether you have electric or gas defrost as this makes a big difference in regards to temrmination temps and where are you getting you termination from i.e pressure switch, coil temp or air temp.. I agree one defrost per day is best.
    You said you had 288 ft of case , are these piped as individual branches and if so do they defrost at different times and do you have branch dividers between the relevant cases?

  15. #15
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Coffin Case Woes

    Just dawned on me that you are using GWIT cases which are "Twin" cases. You might want to make the defrosts simultaneous for each side of case. Picture this: One side is circulating moist defrosting air while the other is cold. It is very likely that the insulated partition between the two discharge flues is permitting the moist defrosting air to condense on the common wall because the other side is refrigerating.

    This moisture refreezes and rebuilds after each defrost.

    If you cannot simultaneously defrost these cases, then I strongly recommend that you have a single, long defrost once a day during off hours.

    You absolutely must let the fans run to permit the de-icing of the flues and drain pan.

  16. #16
    Join Date
    Apr 2006
    Location
    UK
    Posts
    77
    Rep Power
    19

    Re: Coffin Case Woes

    We had same problem on electrulux cases.The construction of the case meant the air off evap space was galvanized steal.This would stay very cold and when the moisture from the defrosted coil passed over it.It would freeze to it.We would move the defrost termination stat coil into the evap. And Set it to 7deg term this allowed the full coil to defrost without over heating it.The newer cases came with a heater in the air off space.Also if there is more than one case put a system divider in to stop air migration from one case to the other.4 defrosts a day 7deg termination 20mins max was the standard within are specifications.If we needed to change that we would have to give a good reason.

  17. #17
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Coffin Case Woes

    Andy T, If it works for you, let it work for you. I am not one who suggests fixes for things people are happy with. But I hope you can see how much farther you can spread the duration between defrosts just in case a future complaint arises.

    But a happy story is to arive at any time of day in a store and walk with the frozen manager checking the quality of his product, without making an apology to a defrost.

  18. #18
    Join Date
    Sep 2005
    Location
    us
    Age
    64
    Posts
    5
    Rep Power
    0

    Re: Coffin Case Woes

    typically a case will exit defrost in one of 2 ways. Either the defrost termination (Temp) or by time (back-up for safety). If the defrost termination has failed or is located in the wrong area the system will remian in defrost until it terminates in time. This situation is usually how ice forms in the discharge (the heaters actually cause the water coming off of the coil to steam, which rolls out into the discharge).

  19. #19
    Join Date
    Aug 2009
    Location
    Dallas
    Age
    59
    Posts
    11
    Rep Power
    0

    Re: Coffin Case Woes

    Hussmann recommends one defrost a day, 60 mins if electric defrost (finned heaters on air entering side of coil), 26 mins if hot gas + 5 min drip, 35 mins if Koolgas + 5 min drip. NEVER turn off the fans, NEVER cover the top of the cases, ALWAYS defrost both sides of a wide island case at the same time. Good luck to ya looking for mint GWI or GWITs. They haven't made them in 20 yrs, any you find now are usually on 3rd or 4th install

  20. #20
    Join Date
    Aug 2009
    Location
    Dallas
    Age
    59
    Posts
    11
    Rep Power
    0

    Re: Coffin Case Woes

    Also I've never seen one with any kind of termination on it, make sure all the fan blades are moving air the right way and not flattened out and lastly all the baffles or honeycombs that direct the airflow must be in place and clean. Those thing are energy hogs, I cant believe anyones still using them.

  21. #21
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Coffin Case Woes

    my back hurts thinking about em
    mmm to beer or not to beer...........lets drink breakfast

  22. #22
    Join Date
    Aug 2009
    Location
    Dallas
    Age
    59
    Posts
    11
    Rep Power
    0

    Re: Coffin Case Woes

    Ahh yes, Guinness. Its so much more than just a breakfast drink

  23. #23
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: Coffin Case Woes

    Quote Originally Posted by displaced paddy View Post
    Hussmann recommends one defrost a day, 60 mins if electric defrost (finned heaters on air entering side of coil), 26 mins if hot gas + 5 min drip, 35 mins if Koolgas + 5 min drip. NEVER turn off the fans, NEVER cover the top of the cases, ALWAYS defrost both sides of a wide island case at the same time. Good luck to ya looking for mint GWI or GWITs. They haven't made them in 20 yrs, any you find now are usually on 3rd or 4th install
    all the drawings i have seen say that fans should stop when term temp has been reached, then they come back on after time has elapsed!

  24. #24
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Coffin Case Woes

    here here paddy,bottoms up.
    gluk gluk gluk ahhh
    mmm to beer or not to beer...........lets drink breakfast

  25. #25
    Join Date
    Aug 2009
    Location
    Dallas
    Age
    59
    Posts
    11
    Rep Power
    0

    Re: Coffin Case Woes

    I think they assume the warm moist air will rise out of the case(very low velocity air curtain) I've never heard of anyone stopping the fans after defrost, why would you? I've worked on hundreds of these and never heard of any fan controls at all. The problem, if the coil is clear, is usually improper airflow from fans,blades or honeycombs, or air curtain disturbance from a/c grilles or door openings

  26. #26
    Join Date
    Nov 2006
    Location
    India
    Posts
    7
    Rep Power
    0

    Re: Coffin Case Woes

    I had a simlar problem at one of the site. The basic thing about the fan operation in Freezer display case is as below

    Freezer Display with glass doors: Fan Off during defrost.

    Open Freezer Display: Fan "on" during defrost to maintain the air curtain.

    We have increased the evaporating temperature from -36 deg C to -33 deg C and increased the defrost duration from 20 minutes to 35 monutes. Since the store humidity condtions are not being maintained, we were forced to go for more number of defrosts than recommended. With this arrangement whatever little frost forms on the supply grill during the cooling cycle gets melted during defrost cycle and we could solve the problem.

Similar Threads

  1. crank case heaters in scroll compressors
    By abbasi in forum Fundamentals
    Replies: 19
    Last Post: 03-08-2010, 03:04 AM
  2. An A/C system for my computer case... can it be done ?
    By electro in forum CPU Overclockers
    Replies: 219
    Last Post: 19-06-2008, 06:19 PM
  3. hotgas and crank case pressure regulator
    By abbasi in forum Fundamentals
    Replies: 8
    Last Post: 27-02-2006, 01:54 PM
  4. Crank case pressure regulating valve
    By Mahmoud in forum Fundamentals
    Replies: 9
    Last Post: 30-09-2005, 02:23 AM
  5. Compressor for island case
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 14-08-2005, 12:08 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •