Results 1 to 14 of 14
Thread: Mnet tool
01-12-2013, 07:25 PM #1
Mnet tool
Looking for info on what each section of the maintenance tool is when monitoring the outdoor unit
any help
cheers
01-12-2013, 10:59 PM #2
Re: Mnet tool
I found that the easiest way to get your head around all the data the Mnet tool throws at you is to get a print out of the refrigerant flowchart from the service manual of the unit.
All the sensors, valves and their locations are on the flowchart and then it is easy to understand the data displayed on the screen.
(But then again, I'm an old fart that doesn't care much for computer based diagnosing)
02-12-2013, 01:23 PM #3
Re: Mnet tool
From wired controller you can diagnosing - Toshiba (need SM), Sanyo ( need SM), ME (not all, most of info from outdoor unit, +SM), MHI (only knowing of Eng. language), Samsung - forgot...( last one was diagnose with notebook + S-Net) Daikin (my favorite) )))) without checker run away. Hitachi work fine/never see them in work. General never try to look parameters in controller. All that systems try to diagnose with soft + notebook, its more comfortable.
Chine masters of VRF is bad. Only GREE not bad.
02-12-2013, 09:07 PM #4
Re: Mnet tool
image.jpg This system is low on gas I know but I'm looking to find out what each section on the outdoor section means I can get the sensors from the flow chart just need to know the rest
cheers
03-12-2013, 06:37 AM #5
Re: Mnet tool
If you click on the help section on the monitoring tool programme it will tell you what the different parameters mean.
The system isn't showing any obvious signs of SOG issues as far as I can see although the compressor hasn't yet ramped up to target condensing pressure of 28bar.
The compressor discharge temp isn't excessively high and most indoor units seem to be heating
At the time that screenshot was taken how long had it been running in heat mode.
Lastly have you checked the diversity of the system because it does look to be quite high?Last edited by marc5180; 03-12-2013 at 06:42 AM.
Marc
03-12-2013, 06:38 AM #6
Re: Mnet tool
Sorry, dont understand what you need )
p.s. you need to know what means sensors and valve in outdoor\BC ?
03-12-2013, 10:25 AM #7
21-01-2014, 06:39 PM #8
Re: Mnet tool
Hi Marc 5180
just getting back to what you said there about the diversity of the unit .what exactly did you mean by this
cheers
21-01-2014, 06:58 PM #9
Re: Mnet tool
indoor capacity exceeds outdoor capacity- therefore if all indoors ask for 100% demand then the outdoor can only give say 75% demand so a few indoors wont do much until the demand drops( as rooms reach setpoint)
unless mark was referring to this!
http://www.diversityofficial.com/
21-01-2014, 09:35 PM #10
Re: Mnet tool
Yeah what Install said.. Are you still having problems with it?
Haha I like it IM .The difference between genius and stupidity is that genius has its limits.
Marc
22-01-2014, 08:15 PM #11
Re: Mnet tool
How do you get the Mnet tool? mitsi partner?
22-01-2014, 09:28 PM #12
Re: Mnet tool
Become a Mitsi partner, attend the basic install/servicing course, the advanced servicing course, then the Mnet service tool usage course and pay £900.00 for the software with a one year licence. Then you are good to go.
Bedford. Now retired and trying to relax.
22-01-2014, 10:01 PM #13
Re: Mnet tool
Or have friends in the right places
Marc
23-01-2014, 11:37 AM #14