Been to site to look at a chiller fault. Both circuits tripping out on LWT sens fault. No manuals on site. Looked at the PCB two red LEDs on top right both lit. Any ideas.
a problem shared is a problem halved
03-03-2006, 02:18 PM #2
Re: York Recip Millenium Chiller
check the two wires sensor LWT,for loose connection , or corrosion , check its connector, or replace the connector with normal screw type connector, repair the wires if damage, or replace the thermistor.
03-03-2006, 06:06 PM #3
Sorted it out now thanks. LW temp sensor had to be removed and the chiller run down to design temps before replacing it. I think it had gone off on a low current/MP/HP fault making the water temp rise too high
Thanks for the replya problem shared is a problem halved
15-07-2006, 12:01 PM #4
The latest EPROMīs resolve the problem as they allow the chiller to run longer before tripping, thus allowing the water temp to lower.
16-07-2009, 09:03 AM #5
having simular problem cant find manuals for this machine, cpu trouble and remote control problem trouble,ugg if you find something please let me know,, clarkster
16-07-2009, 09:47 AM #6
I've got manuals for most of the York machines, all the Carrier and Trane ones
16-07-2009, 10:22 PM #7
mmm, ive had that fault a few times and changed several sensors. think i'll take the connecter out and solder straight through. - dont suppose anyone got the specific manual for the york 'ISN millenium recip pak' controller, its a bitch to get hold of.
16-07-2009, 11:03 PM #8
Koolio
it may not be the connection, water in the pockets kills the feckers as well, change them on a monthly basis on the YCAL chillers.
al
17-07-2009, 02:56 PM #9
hi i have the manual will try to upload on sunday
22-07-2009, 09:16 PM #10
22-07-2009, 09:18 PM #11
22-07-2009, 09:21 PM #12
bearing in mind - i have the manual for the chiller / it's the manual for the ISN millenium recip pak controller im after.
28-07-2009, 07:21 PM #13
hi there i sent u the manual via email hope it is ok if notlet me know i will try to get it
http://dl.owneriq.net/b/bd843a30-488...b4334830e0.pdf try this in case what i sent was not okLast edited by goshen; 28-07-2009 at 07:33 PM.
York Millenium Screw Chiller
By iceman007 in forum Industrial CompressorsReplies: 26Last Post: 15-01-2011, 11:56 PM -
York Chiller
By HVACGod in forum CommercialReplies: 12Last Post: 11-09-2010, 06:05 AM -
York Chiller
By RubenJLL in forum Trouble ShootingReplies: 20Last Post: 18-04-2008, 04:08 PM -
York Screw Chiller How low will it go?????
By bruceboldy in forum Industrial CompressorsReplies: 11Last Post: 10-08-2007, 10:29 PM -
York process chiller repairs
By Matt in forum CommercialReplies: 5Last Post: 23-03-2004, 11:07 PM