    Compressor shaking after air conditioner shutting down



    hi
    i received an old LG heatpump split ac unit
    that had leakage because of cracked capillary tube
    i cut 1 cm of the capillary then i weld it
    made vacuum for 30 minutes then
    charged it by weight
    and it cool very good
    problem is that when i shutting down them unit
    compressor keep shaking for sometimes
    30 seconds
    5 seconds
    and sometimes not
    what is the problem or that is ok

    in this video compressor shake up for 3 second only






  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Compressor shaking after air conditioner shutting down

    Refrigerant is expanding from high pressure side and turns motor backward until pressure equalize. Faulty (stuck) discharge valve at high side.

    Last edited by nike123; 21-08-2013 at 08:41 PM.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Compressor shaking after air conditioner shutting down

    http://www.ra.danfoss.com/TechnicalI...A5.02%20vs.pdf
    fit another non return valve on the discharge line- stop the rattlin and prevent pipe fracturing
    make sure u fit it the correct way round

  4. #4
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    623
    Rep Power
    17

    Re: Compressor shaking after air conditioner shutting down

    ok
    if i left the unit working at this way
    what will happen except rattlin & pipe fracturing

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Compressor shaking after air conditioner shutting down

    more repairs, and more posts on here!

  6. #6
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    36
    Posts
    623
    Rep Power
    17

    Re: Compressor shaking after air conditioner shutting down

    ok
    the solution installing discharge line check valve
    thank u all